What about holding registers?
@SEWEurodriveUSA
@SEWEurodriveUSA 14 сағат бұрын
Hello. The Movitrac LTP-B does support Modbus RTU with register functions if that is what your question was about. Here is the excerpt from the manual about it: "The inverters support communication via Modbus RTU. Use the function "Read Holding Register (03)" for reading and the function "Write Single Register (06)" for writing. The function "Write Multiple Register (16)" is also available for PO data words 1-5." This is explained on pages 217 - 219 of the manual linked here: download.sew-eurodrive.com/download/pdf_u/31554814.pdf The Modbus RTU setup parameters start back on page 213. If you need to speak with someone on the phone about this you can contact your nearest SEW office at this link and ask for Electrical Support when calling in. www.sew-eurodrive.de/meta-pages/contacts_worldwide.html
@joshuamarpa1220
@joshuamarpa1220 11 күн бұрын
Hi i have a fault 86 , memory module
@SEWEurodriveUSA
@SEWEurodriveUSA 13 сағат бұрын
Hello. The fault 86 indicates that the Movidrive doesn't detect the red colored memory module on the top of the inverter control section. This module has a "stop sign" logo printed on it. This can come from the memory module being removed and turning the inverter on. Or from a hardware issue. If you can confirm that the memory module is installed and you still get the fault after cycling the voltage. Then the other things you can try are to factory default the parameters and then reload them from a previous backup (this is best done with the MotionStudio software, and you must have a known good backup of the parameters before setting it to a default condition). Or you can send the Movidrive in for Electronic Evaluation to see if it can be repaired by SEW. Here is where you can locate your nearest SEW office for Electrical Support. www.sew-eurodrive.de/meta-pages/contacts_worldwide.html
@jeongtaeho8050
@jeongtaeho8050 27 күн бұрын
I love you
@iancastro2016
@iancastro2016 2 ай бұрын
HI MY MOVITRAC INVERTER WAS H1 LIGHT INDICATOR ON .ILL ALREADY CHANGE ALL CABLES BUT STILL THE SAME ISSUE.ANY SUGESTION ? THANK YOU
@SEWEurodriveUSA
@SEWEurodriveUSA 2 ай бұрын
Hello. This would be easier to troubleshoot over phone support since there are several different versions of the Movitrac inverter. We would need to know a lot more information to assist in troubleshooting. You can contact your nearest SEW office and ask for electrical support so they can talk with you about this. Here is where you can find that contact information. www.sew-eurodrive.de/meta-pages/contacts_worldwide.html
@schmidtjohnson1826
@schmidtjohnson1826 2 ай бұрын
What about W.9 & W.9HG? And W10-30?
@SEWEurodriveUSA
@SEWEurodriveUSA Ай бұрын
Hi @schmidtjohnson1826. Thank you for your suggestion. We just released a new podcast that should answer these questions. kzbin.info/www/bejne/jXXKaKWsmL6CY9U
@schmidtjohnson1826
@schmidtjohnson1826 Ай бұрын
@SEWEurodriveUSA perfect
@karimtech1343
@karimtech1343 2 ай бұрын
Fault number 2 how to operate Automode
@SEWEurodriveUSA
@SEWEurodriveUSA 2 ай бұрын
Hello @karimtech1343. There is not a flashing fault F02 for the MDX61B Movidrive B. If the 7-segment display is showing a 'solid' number 2 that indicates that the Movidrive is missing the 'Enable' signal. This is a normal condition to see while the Movidrive is operating. The Enable signal could be needed on the digital inputs or from the fieldbus. It depends on how it is configured. Please contact your nearest SEW Eurodrive office using this link and ask for Electrical Support so they can offer you telephone support. www.sew-eurodrive.de/meta-pages/contacts_worldwide.html
@vladoovg
@vladoovg 2 ай бұрын
Encoderless servomotor ? Something like waterless water i guess.
@SEWEurodriveUSA
@SEWEurodriveUSA 2 ай бұрын
Hi @vladoovg. Permanent magnet servomotors are preferred for applications requiring faster running speeds, precise positioning or higher starting torque from standstill. So if the application doesn't require the precision of encoder feedback for positioning but the application specifically needs a fast speed or higher starting torque. An encoderless servomotor could be an option to consider and save the cost of the encoder if it isn't needed. I hope this helps understand the purpose of an encoderless servomotor.
@vladoovg
@vladoovg 2 ай бұрын
@@SEWEurodriveUSA I must respectfully disagree with the use of the term 'encoderless servomotor.' By definition, a servo motor operates within a closed-loop system that requires feedback from a sensor, typically an encoder. This feedback is crucial as it enables real-time monitoring and adjustment of the motor’s position, speed, and torque. Without this feedback, the motor cannot be classified as a true servo motor.The term 'servo' inherently implies 'feedback-controlled,' and removing the encoder eliminates the closed loop, effectively rendering it a standard induction or synchronous motor, even if it employs advanced control methods. While some sensorless technologies can mimic servo behavior, they do not fulfill the complete requirements of a servo system in the strictest sense. Additionally, while EMF control can be utilized by frequency drives to manage motor performance, this alone does not qualify the motor as a servo motor. Furthermore, the use of terms like 'encoderless servomotor' can sometimes be misleading and is driven by marketing strategies to appeal to a broader audience. It’s important to maintain clarity in terminology to avoid confusion and to ensure that users understand the actual capabilities and limitations of the technology they are considering. In summary, without an encoder or another form of feedback, we cannot accurately refer to a motor as a servo motor.
@muhammadrafianazim2468
@muhammadrafianazim2468 3 ай бұрын
can we programm that vfd without usb11A?
@SEWEurodriveUSA
@SEWEurodriveUSA 3 ай бұрын
@muhammadrafianazim2468. Hello. It is potentially possible to commission the Movidrive MDX61B inverter without the USB11A. If the Movidrive is connected to the fieldbus you could use an RJ45 ethernet cable for example. However, if you only have the DBG60B keypad it will be very limited in the options and motor types you can commission only using the DBG60B keypad. If you wish to do IPOS programing you must have the USB or Ethernet fieldbus option to connect the PC to the Movidrive. The USB11A part number: 08248311 has been discontinued (but works fine for Movidrive B if you can locate one) and it now is replaced by the USM21A part number: 28231449. Which works for the Movidrive B and new MOVI-C devices. Here is our KZbin video showing how to use the DBG60B keypad on the Movidrive B. kzbin.info/www/bejne/qoq6qJuqpciFo6cfeature=shared
@jkavillan
@jkavillan 3 ай бұрын
Hi sir, I have an error F122, " Absolute Encoder Option" . Suberror 16640. So due to this error i could not jog the lifter down by using manual operation in movitools. I need to jog it down so i have access to replace the external encoder. Please advise and thank you in advance.
@SEWEurodriveUSA
@SEWEurodriveUSA 3 ай бұрын
Hello @jkavillan. In this situation it may be challenging to manually move the application since the fault is limiting the axis to operate. You can attempt to connect a PC to the Movidrive B and operate it manually from the software but it may still continue to fault and inhibit the ability to manually operate it. Watch the Session 6 Lab 4 video on manual operation starting at minute 17 30. kzbin.info/www/bejne/qWmTZWeHaKimbK8feature=shared&t=1050 If it continues to fault in manual operation you may have to re-commission the Movidrive parameters to deactivate the encoder settings so it is ignored by the Movidrive. This process may be very tricky to do without help from SEW-Eurodrive since you will need to backup the parameters before making any large parameter changes like that, and encoders can be connected in several different ways to the Movidrive. Please contact your nearest SEW-Eurodrive office and ask for Electrical Support so they can talk with you about this situation. www.sew-eurodrive.de/meta-pages/contacts_worldwide.html
@jkavillan
@jkavillan 3 ай бұрын
@@SEWEurodriveUSA thank you so much
@miken1574
@miken1574 3 ай бұрын
Could you guys please do a series on the SEW Movifit vfds? Covering topics like: brake & rectifier, STO, brake resistors, thermistors/thermostats, wiring of the internal 24v circuits. Thanks a lot.
@SEWEurodriveUSA
@SEWEurodriveUSA 3 ай бұрын
@miken1574. Thank you for the suggestions. That lets us know what videos would be helpful. The Movifit Generation B product line is being phased out by 2026, so there is not a plan to create any new training videos for it. It is being replaced by the Movi-C Decentralized generation that we have been creating videos for. However, we have previously offered in-person trainings covering the Movifit product line. Here are some links to access that self-study material. I hope this is helpful. In-person Training Workbooks and Presentations (password: movifit2024)(link is live until November 14, 2024): transfer.sew-eurodrive.com/download?id=dMLwH8Sr4V Online SEW-Eurodrive Germany MOVIFIT FC/MC/SC - Overview: download.sew-eurodrive.com/learning/MOVIFIT_FC_MC_SC_Overview/EN/index.html Online SEW-Eurodrive Germany MOVIFIT® FC/MC/SC - Types, operating principle and technical key data: download.sew-eurodrive.com/learning/MOVIFIT_FCMCSC_Types_oper_princ_tech_key_data/EN/index.html
@tonybischoff3608
@tonybischoff3608 3 ай бұрын
Hello, I have an issue with a drive. I cannot figure out how it gets the ccw or reverse direction. It is a compiler based and is all fieldbus communications. Is the set point possibility supposed to be negative? I know parameters 35 is for switching direction. Bit we have another machine that uses this drive and that parameter doesn't change.
@SEWEurodriveUSA
@SEWEurodriveUSA 3 ай бұрын
@tonybischoff3608. That is hard to say without seeing the parameters/IPOS program. Generally, for fieldbus control the speed or position setpoint is a signed integer (i.e. negative/positive depending on direction of travel). If it is only a jog mode control then possibly there are separate bits or inputs for the CW vs CCW directions. You can look at parameter P100 & P101 to see where the Movidrive is looking for the setpoints. Also, in MotionStudio there is a tab for "IPOS Information" above the "0.. Display Values" parameter folder. Click on that and view the text box to see if it is one of SEW's Application Modules or if it is a custom IPOS program. Our phone support is free if you would like to call your nearest SEW office and ask for Regional Engineering - Electrical Support. They can provide you with an email as well so they can inspect the parameters while you're on the phone. www.seweurodrive.com/contact_us/find_cs_sales_distributors/sales_default_nmc.html
@RideWithAnthony
@RideWithAnthony 3 ай бұрын
is it normal to have oil leak from oil seal?
@SEWEurodriveUSA
@SEWEurodriveUSA 3 ай бұрын
@RideWithAnthony it is not normal for an oil seal to leak. Oil seals are wear items and parts of the gearmotor that need to be replaced when the time is due. The length of time the seal will last depends on several factors such as operating environment, shaft speed, oil type, and any external debris contacting the seal surface. If you find a unit with a leaking seal it should be replaced. If you provide your local SEW-Eurodrive customer service with the S.O.# from the gearmotor nameplate they can provide you with the part number and type of seal you need to use to replace it. Here is a map of the SEW offices in in the USA. Click the region on the map for the contact details to appear. www.seweurodrive.com/contact_us/find_cs_sales_distributors/sales_default_nmc.html
@asharsaeed1880
@asharsaeed1880 3 ай бұрын
I have an MC071B drive, Which I've been trying to learn how to control work on my own so I'm stuck in a 24 V operation state I don't know how I can change the operation state, So I need your help and last but not least Can you provide me with any training regarding this.
@SEWEurodriveUSA
@SEWEurodriveUSA 3 ай бұрын
Hello @asharsaeed1880. We do not have any training videos for the Movitrac MC07B inverter. However, it is almost identical to the Movidrive MDX61B in how you commission and change the parameters. The biggest differences are that the MC07B will use a different wiring diagram, and the keypad is different. If the inverter shows 24V on the display and you have 480V switched on then possibly the STO ("Safe Torque Off") X17 jumper plug on the bottom of the inverter is not installed. You can see this on the wiring diagram on page 205 of the MC07B System Manual here. download.sew-eurodrive.com/download/pdf_u/31960421.pdf. Here is a brief online e-learning module for the Movitrac MC07B. download.sew-eurodrive.com/learning/MOVITRAC_B_Overview/EN/index.html If you rather speak with someone about this you can find your nearest support office using this tool here. www.sew-eurodrive.de/meta-pages/contacts_worldwide.html
@tanvirul8390
@tanvirul8390 4 ай бұрын
Excellent explanation.
@mineshkapadia9023
@mineshkapadia9023 4 ай бұрын
You're just great. 🎉
@lp1082
@lp1082 4 ай бұрын
Hi. I loved the interface and the workflow , may I ask which sofware company did you ask to buit it?
@lbribr5963
@lbribr5963 4 ай бұрын
Good & Helpful
@satishbeniwal1601
@satishbeniwal1601 4 ай бұрын
superb
@satishbeniwal1601
@satishbeniwal1601 4 ай бұрын
superb
@sethkazzim731
@sethkazzim731 5 ай бұрын
I need this
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Good video
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Good video
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
The best video in the world
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
It helped me a lot !!
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Good video thanks
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Thanks haha
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Excellent !!
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Thanks it helped me a lot !!
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Thanks it helped me a lot
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Thanks it helped a lot
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Good video
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Great video
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Good video
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Great!!
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Thanks u
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Good
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Good video
@Jeongtaehoi
@Jeongtaehoi 5 ай бұрын
Thanks
@invidious77
@invidious77 5 ай бұрын
Could you include a link to your website where we can download the GSD files we see in use in this video? I have tried contacting SEW directly for assistance in finding the proper GSD file for these drives and have had lackluster responses. Thanks.
@SEWEurodriveUSA
@SEWEurodriveUSA 5 ай бұрын
Hello. Thank you for letting us know we didn't have links in the description box. Do you know which devices you specifically have so we can see if there is a GSD or GSDML file available for it? Here are some direct links to our website for the list of GSD and GSDML files. There are many options shown so you'll have to carefully examine the list to find your model type with the correct fieldbus type it uses. Click the "arrow" on the left to expand the item to show the download button. GSDML Files for PROFINET: www.seweurodrive.com/os/dud/?tab=software&country=US&language=en_us&software_group=17 GSD Files for PROFIBUS: www.seweurodrive.com/os/dud/?tab=software&country=US&language=en_us&software_group=6
@kerlinjoelespinozavaldizan3408
@kerlinjoelespinozavaldizan3408 6 ай бұрын
se puede controlarr desde el mismo movidrive de manera remota?
@SEWEurodriveUSA
@SEWEurodriveUSA 6 ай бұрын
Hello. We don't understand that question. Could you elaborate further? If you would prefer local support please find your nearest engineering/sales office at this link. Our telephone support is free of charge. www.sew-eurodrive.de/meta-pages/contacts_worldwide.html
@kerlinjoelespinozavaldizan3408
@kerlinjoelespinozavaldizan3408 6 ай бұрын
Hola podrian enviara el link del manual completo para poder usar, quiero resetear a fabrica y no puedo
@SEWEurodriveUSA
@SEWEurodriveUSA 6 ай бұрын
Hello. Here is the link to the Movidrive B System Manual in English below. You can do a factory reset using parameter P802 and set it to "Delivery State". Just know that it will delete everything. So you would need to back up any IPOS programs or parameters first before doing the delivery state. There is no final warning when you change P802 to "Delivery State". download.sew-eurodrive.com/download/pdf_u/27793230.pdf
@dlp-r2r
@dlp-r2r 6 ай бұрын
10/10 Un verdadero entrenamiento
@loukrizdjamel2334
@loukrizdjamel2334 6 ай бұрын
thanks
@dlp-r2r
@dlp-r2r 6 ай бұрын
Excelente 10/10
@loganathanm1229
@loganathanm1229 6 ай бұрын
Excellent 👌
@juantony100
@juantony100 6 ай бұрын
Hello, the addresses where to send the control words are 400001 from now on right? I have not found in the manual that it refers specifically to that number. Do you have any source code for PLC S7 1200? Thank you. Greetings from Argentina
@SEWEurodriveUSA
@SEWEurodriveUSA 6 ай бұрын
Hello. We don't have specific examples for Siemens process data words but the manual shows standard Modbus RTU messages if that is what you need descriptions on how they are formatted. Here is the 2023 Product Manual for the Movitrac LTP-B. download.sew-eurodrive.com/download/pdf_u/31554814.pdf Process Data Parameter Configuration: Page 95 - 97 Modbus RTU Message Examples: Page: 102 - 105 We have an office in Argentina if you would like to speak to someone in engineering on the phone. Here are those contacts. tel: +54 332 745 7284 www.sew-eurodrive.com.ar/meta-pages/web_contact_form_in_page.html
@-Automations
@-Automations 6 ай бұрын
hi. thanks for your video. i need to solution for f09 error cod ("wrong operating mode selecting"
@SEWEurodriveUSA
@SEWEurodriveUSA 6 ай бұрын
Hello. Error code F09 relates to the motor startup procedure. You can watch this video here on how to do a motor startup. kzbin.info/www/bejne/rpfZXmWEqbaAhLsfeature=shared&t=225 Depending on the model type of the motor you have installed the Movidrive parameters have to be correct for that type of motor. The operating mode is parameter P700 but you should not change it directly. It needs to be done through the startup procedure shown in the video linked above. Once you input the values in the startup and click "download". Those parameters will be corrected in the background to match with the motor that is installed. It's helpful to get a picture of the motor's nameplate to aid you during the motor startup procedure.
@nandukrishnan6746
@nandukrishnan6746 6 ай бұрын
Sir,can I check error no 8 with this keypad??
@SEWEurodriveUSA
@SEWEurodriveUSA 6 ай бұрын
Hello. Yes. Fault F08 can be displayed on the keypad through the fault history. The fault history is in parameters 080 through 084. Parameter 080 is the most recent fault and P084 is the least recent. You can look in the fault history and determine if the F08 was caused by high output current or something else. Fault F08 is the most common fault that can happen on the Movidrive B. In this video linked here you can see some common problems and resolutions to the F08 fault. kzbin.info/www/bejne/sIapkGRomKuJbNEfeature=shared&t=969
@NGUYENTUANDKC08102
@NGUYENTUANDKC08102 7 ай бұрын
hi mr , i have problem with F14 code 27 , can you share me the way to trouble it!
@SEWEurodriveUSA
@SEWEurodriveUSA 6 ай бұрын
Hello. Fault F14 is related to errors with the motor encoder. Specifically, with suberror 27 this is indicating a loose connection at the Movidrive or at the motor. It could also be a defective motor encoder. Is the fault sporadic or constant? If the fault is sporadic then it usually indicates a wiring issue with the encoder cable between the Movidrive and the motor encoder. This could be a loose wire, incorrect cable shield connection to earth ground at the Movidrive and motor, or a broken/cut wire. If the fault is constant and there are no obvious issues with the encoder cable connections. Then it could be defective hardware where you would need to replace the motor encoder or the complete gearmotor if is a permanent magnet servo motor for example. At 21:02 in this video are some tips for checking the cause of the error F14.