@MrSpidey72 6 жыл бұрын
Brilliant! Had an e20 error on boiler, so ordered a thermistor for £3.99 and that's the boiler fixed!! What a superstar-thank you for the video 😀
@johnkerr8019
@johnkerr8019 7 жыл бұрын
II I had a hat on I'd take it off, well done!!!! You have systematically worked your way through a fault diagnosis and repair.Ii know some so called engineers who may not have completed that job as competently. Why pay for someone who in my experience doesn't always replace the correct part or mis-diagnosis the fault and replaces the incorrect part. This has been hugely helpful and interesting and informative video. I may have missed this on the video, but was there a fault code displayed at the start of the problem.
@bobchadwick8629
@bobchadwick8629 3 жыл бұрын
Just watched your videos. I had the same problem. Bought the motor for £35 Yippee! I have heating back. Well done mate! My spring was rusted solid. When I opened the motor though it sprung apart sending bits everywhere so if you try this be VERY careful opening the motor! I had no error messages. 2 Years ago I replaced the 3 way valve assembly by watching similar videos! I have saved about £400! To the 'knockers' - 'Knickers! You never learn anything if you don't try.
@MrMeltedwellies
@MrMeltedwellies 3 жыл бұрын
Glad I could help
@RailwayTavern
@RailwayTavern 2 жыл бұрын
Good video. I have the same boiler and currently have hot water but no heating. Putting it in service mode (to change high/low flame) has got my heating working again however and whilst in service mode it seems fine but the boiler cycles on and of with the flame. Otherwise when you call for heating from the wireless stat the actuator valve opens but the boiler doesn’t respond. No led light on heating. No pump running. Nothing. But when in service mode it’s all working fine and rads warm up. Any idea what’s up with it? Cheers
@110Griff
@110Griff 6 жыл бұрын
heres the thing, if that was a wet pocket sensor, that water would of come out at a pressure of about 1.5 bar, not only that, it was at 80 deg temp you could of ended up with serious burns. you would have also flooded the boiler probably damaging the pcb and other electrical components, you got away with it, but you were lucky. I would of checked the divertor motor first to make sure it was moving to the heating position. the water is not getting away from the boiler, check the heating flow pipe to see if it's getting hot.
@cristiandiaconescu6411
@cristiandiaconescu6411 7 жыл бұрын
Hey man , Thank you very much for your advice , I had an error E 50 so ive got the 2 sensors that I needed ,BAXI DUOTEC 24 28 33 & 40 HE & HE A SYSTEM NTC SENSOR THERMISTER 5114725 NEW and the second one Mouse over image to zoom BAXI-DUE-TEC-24HE-28HE-33HE-40HE-TEMPERATURE-SENSOR-THERMISTER-5114725, so thanks to you I've turned the water off hahaha Cheeres man
@cristiandiaconescu6411
@cristiandiaconescu6411 7 жыл бұрын
I've got mine from eBay from £4 each , you need to turn the water off only if u change the BAXI-DUE-TEC-24HE-28HE-33HE-40HE-TEMPERATURE-SENSOR-THERMISTER-5114725, not for the NTC one but u'll have to replace bought any way
@James-nk4sj
@James-nk4sj 4 жыл бұрын
I think it was dry because the boiler was not on hotwater mode - mine was not dry - and one of the taps was still on also... its difficult to get the thermister back in with it pissing out water... The new one came with a washer but the old one did not. I think the washer stops it fitting properly so it was extra difficult to figure that out.
@abdulwahedy5528
@abdulwahedy5528 2 жыл бұрын
When you should replace this boiler? It mean after how money years we should replace it?
@andymartin86
@andymartin86 7 жыл бұрын
Good on you Mark for having a go. I don't get why there is all the negativity. He's not touching anything gas related and is well within his right to do what he is doing. If only more people had a go at solving problems like this people would actually learn about things and be more knowledgable in the future, rather than the throw away society we live in. Its good that you have followed a logical path and ended up finding the cause of the fault learning along the way. It's this method that makes people learn and next time you will be quids in. Well done.
@MrMeltedwellies
@MrMeltedwellies 7 жыл бұрын
Thanks very much Andrew i love to learn ATB mark
@lord3296
@lord3296 7 жыл бұрын
Hi Andrew you stated he isnt touching anything gas related and is within his right that is in fact very wrong. Just for everyone knowledge he has removed the cover to the boiler that cover has a seal around it this can allow products of combustion into the room if not fitted correctly therefore you do need to be gas safe to undertake the work this gentleman has done.
@jaxmar88
@jaxmar88 7 жыл бұрын
In my spare time I'm going to take up brain surgery, surly it can't be that difficult :-)
@justsendmelocation5068
@justsendmelocation5068 7 жыл бұрын
Once you take the case off your interfering with the boiler integrity.
@brotherzaq
@brotherzaq 4 жыл бұрын
@@justsendmelocation5068 Only according to the 'rule' writers whose vested interest is in stopping you from DIY. Stick to footie mate.
@d4ngerous4
@d4ngerous4 Жыл бұрын
Hi mark, my central heating not working, its currently showing the flame light as orange and the tap water light is green, both solid, the central heating light is off, when i put on service mode it heats up the radiators no bother, but problem is it doesnt stay on in service mode, do you have any ideas?? The heating was working fine last night, ive also tried to reset. Any help appreciated, cheers
@michelangelosghost2707
@michelangelosghost2707 3 жыл бұрын
Brilliant video. Very helpful
@tonycosgrove6433
@tonycosgrove6433 5 жыл бұрын
The mad professor comes to mind.
@dogrob1973
@dogrob1973 8 жыл бұрын
Mate, the heats not getting away from the boiler fast enough. It's not temp sensors, check the pump and quality of water in the heating system (probably black). You have an obstruction in flow, check flow and return valves are fully open and check pipes are getting hot underneath. It's certainly nothing to do with thermostat. Also check the valves on your magnaclean are open if you have recently serviced it.
@MrMeltedwellies
@MrMeltedwellies 8 жыл бұрын
+dogrob1973 thanks for watching
@jamesknowles550
@jamesknowles550 Ай бұрын
Don't tell him anything -- the guys a danger to himself + others !
@drewok1967
@drewok1967 5 жыл бұрын
The part I’m looking for is the left side water tap, has a black tap switch attached to it. The whole of that part is a bit leaky, so need to replace it. Any advised will be great. Thanks in advance.
@dodtaylor4975
@dodtaylor4975 4 жыл бұрын
Hi mark I have the potter ton 24 very similar to yours just no digital temp gauge. Now my problem in no ignition ,replaced the pcb but still nothin only light on is the power light nothing else lights up ,changed the ignitor also still nothing can you shed any light on this prob , there is plenty gas going to boiler central heating is off as not required till December but it won’t fire up anyway ,regards dod
@MrMeltedwellies
@MrMeltedwellies 4 жыл бұрын
Hi Dod sounds like the ignition unit on the gas i don't touch gas so you might have to call a gas engineer soz thanks for watching
@PLBL
@PLBL Жыл бұрын
Is it possible to connect one of these to a smart thermostat?
@mange2
@mange2 6 жыл бұрын
Its funny how there's all these heating engineers (experts) on here telling you don't touch the boiler, and coming up with all sorts of scenarios that don't solve the problem. And these are the very people who want £65 call out and £65 per hour to solve a problem that they don't even understand. Oh and I forgot, plus VAT plus VAT plus VAT and on top of that plus VAT. Do what you want with your own boiler but don't touch the Gas. When all else fails, employ a Doctor, Lawyer or Airline Pilot to fix it, Their hourly rate is much less.
@Han-es8qu
@Han-es8qu 5 жыл бұрын
Bravo
@PlayStation_ACE
@PlayStation_ACE 5 жыл бұрын
Heating engineers want you to give you all your hard earned to them and would probably fault find the same way as this guy's vid. Sometimes you have to change various parts! Its part of the fault finding process. I have Luke warm water but could be caused by 3 or more components.
@rockreel2466
@rockreel2466 Жыл бұрын
@Dave J luke warm water is more than likely caused due to lack of servicing. What is the Net Kw output of your boiler and what reading did you get (m³/hour) at max in service mode. Did you get the correct -ve fp as per MI's?
@jamesknowles550
@jamesknowles550 Ай бұрын
@@PlayStation_ACE Hey most heating engineers spend time and money on training + exams so they can repair boilers correctly leaving the boiler safe to use -- yes we do sometimes have to change more than a fuse , but most engineers will get it safe + working first time -- this guy is a danger to himself + others -- and i'm sure he knows it !!
@davidpotts1778
@davidpotts1778 12 күн бұрын
these dumbs dumbs are all Gas Safe Engineers that are a class of persons!!!!!!! you fuking tool. people like you and this idiot are why houses blow up and kill people!!!!!
@kts64
@kts64 3 жыл бұрын
I have same boiler from council, I had a green light on rad symbol was a Amber light on burner symbol, but now all lights are off, does lights need to be on
@andrewhubbard1971
@andrewhubbard1971 7 ай бұрын
E133 shall I change the ignition sensor
@straighttalknomessing3934
@straighttalknomessing3934 9 ай бұрын
This is my boiler too .. my heating will not come on yet I have hot water . Only upstairs 2 heaters come on .
@phoenixgaminglt4749
@phoenixgaminglt4749 Жыл бұрын
Diverter motor. Hot water but o heating or vice versa its the go to part
@ashvanbro9329
@ashvanbro9329 Жыл бұрын
Great work mate my sister in law has no hot water what would u reckon it was 🤣
@bienio11
@bienio11 6 жыл бұрын
Hi!What does the e1 25 problem mean?
@MazxzaM
@MazxzaM 4 жыл бұрын
My heaters and water is hot, pressure is on 0. I recently moved in and have this boiler. Can you tell me how to put the pressure back in. Thank u.
@Quincy111
@Quincy111 6 жыл бұрын
had on one of these nearly four years, nothing but trouble
@PatrickKelly-lz3pv
@PatrickKelly-lz3pv 5 жыл бұрын
I have had one for ten years no trouble at all
@garytaylor5675
@garytaylor5675 Жыл бұрын
How do you re pressurised this boiler when it has no pressure?
@MrMeltedwellies
@MrMeltedwellies Жыл бұрын
There is a pressure tap under the boiler
@ashleykinrade355
@ashleykinrade355 8 жыл бұрын
is your pump ok? sounds like its banging a bit when getting very hot
@MrMeltedwellies
@MrMeltedwellies 8 жыл бұрын
+Ashley Kinrade hi I think so working great so far but I will keep an eye on it thanks for watching
@karanrai5462
@karanrai5462 2 жыл бұрын
Hi mark how to repressurized potterton pro max boiler?
@danteishimura9189
@danteishimura9189 4 жыл бұрын
Not sure if anyone can help me with the issues I am having with my Potterton Promax Combi 24-28-33, but I cannot find help anywhere. Basically on 05/02/2020 the batteries on the wall timer ran out and I couldn't get new ones until the next day. In the morning I noticed the hall radiator was warm and after looking into this it seems the boiler will go into an emergency mode and create heat to the radiators every few minutes (actually a very cool feature). Anyway I bought new batteries yesterday but for the life of me I cannot get the wireless wall timer unit to sync with the actual boiler. I have tried holding the button on the boiler which gives 2 red flashes and when you let go the red light stays constant for a couple of minutes. I am assuming this is the heater trying to sync with the wireless wall timer? But it just won't connect to it. I even pressed the reset button on the wall timer but still it gives a flashing red light every 15 seconds or so. The landlord has an engineer coming 10/02/2020, but I'd really like to have this sorted sooner if any of you guys have come across this.
@roseward6787
@roseward6787 7 жыл бұрын
I've got a potterton heatmax combi boiler he range the temperature fine on it but heating only comes on when running the hot water any ideas please thanks rose
@aamir3926
@aamir3926 6 жыл бұрын
Rose Ward Same problem here
@sihammsihamm5354
@sihammsihamm5354 4 жыл бұрын
Hello i have the same boiler hot water not working can you help me plz
@ShaynesGames
@ShaynesGames 4 жыл бұрын
How do you get it in high service mode
@straighttalknomessing3934
@straighttalknomessing3934 9 ай бұрын
Also the pressure is what too high on my thermostat. I can’t seem to lower it . And we have 7 radiators yet only upstairs 2 work partially. I can’t afford to buy a new boiler so it would to fix the one I have
@icandodgebullets7869
@icandodgebullets7869 3 жыл бұрын
Can anyone help? I have a 5f error on my boiler and the central heating won't turn off from the thermostat. Hot water is fine but I can constantly hear the boiler rev up every now and again. Any idea on what it could be?
@drewok1967
@drewok1967 5 жыл бұрын
Where can you buy spare parts for this boiler?
@MrMeltedwellies
@MrMeltedwellies 5 жыл бұрын
all on ebay
@davidpotts1778
@davidpotts1778 12 күн бұрын
if this doesnt work il have to ask neil who is a plumber?????? are you gas safe Mark?
@MrMeltedwellies
@MrMeltedwellies 11 күн бұрын
NO just a DIYIST David (plumber didn't turn up so i had a go myself i kept it running for five years)
@gjmheating8857
@gjmheating8857 8 жыл бұрын
gas engineer not plumber! well I certainly didn't learn like that, you could of damaged the pcb or even worse!!
@Han-es8qu
@Han-es8qu 5 жыл бұрын
bull sheet
@NorthernNectar
@NorthernNectar 2 жыл бұрын
Lol gimme your money I’ll rip you off lol
@daryl1751
@daryl1751 4 жыл бұрын
Hi there, ive got the same boiler promax he plus. Its coming up E50 NTC fault, do you no which sensor it is?
@richardturton4526
@richardturton4526 4 жыл бұрын
Hi my boiler has same problem , Did you sort it Thanks
@Hitngan
@Hitngan 4 жыл бұрын
Its the Pump
@dogrob1973
@dogrob1973 8 жыл бұрын
Also stop pissing about with gas boilers!
@MrMeltedwellies
@MrMeltedwellies 8 жыл бұрын
+dogrob1973 cant help it love fixing things just plumbed my son's house from top to bottom had it checked by a pro and all great ;-)
@dani4772
@dani4772 4 жыл бұрын
DELETE THIS VIDEO IT IS SUPER UNSAFE TO DO THIS.
@robertstanway9893
@robertstanway9893 Жыл бұрын
This man obviously doesn't understand the basic fundamentals and guessing
@shahzadkhan-lb3bg
@shahzadkhan-lb3bg 6 жыл бұрын
E50 what that means any one knows??
@sadeqashori3491
@sadeqashori3491 3 жыл бұрын
What 33 e1
@Memories4lifemedia
@Memories4lifemedia 6 жыл бұрын
You do know you are breaking the law by removing the burner case..
@chrisbailey4759
@chrisbailey4759 4 жыл бұрын
Not a law, a statute, common mistake.
@gjmheating8857
@gjmheating8857 8 жыл бұрын
tell gas safe that in fact I will!
@lexmarkakis3087
@lexmarkakis3087 4 жыл бұрын
This guy has no clue what he’s doing only work on boilers if you are gas safe
@kamaluddin1671
@kamaluddin1671 4 жыл бұрын
You haven't got a bloody clue what you are doing and changing thermistors for nothing, get a gas engineer and you can see clearly the boiler is over heating on central heating demand as the temperature is rising then the overheat thermostat activates and shuts off the boiler so the fault is something else which i am not going to tell you about it, it is only for Gas Safe Registered Engineers. you are not competent to touch this gas boiler,
@MrMeltedwellies
@MrMeltedwellies 4 жыл бұрын
I have tried to get a boiler engineer but they never turn up 7 times i even fixed my lads boiler last year because he's got a 2 and 4 year old were freezing their asses of ,i have keeped both boilers going for 4 years now ,i don't touch the gas .thanks for watching and comment
@Mark-lu3tn
@Mark-lu3tn 5 жыл бұрын
Potterton housing estate garbage avoid this crap
@snigie
@snigie 5 жыл бұрын
You have no idea what your doing. Why risk working on a boiler to save money. And your changing perfectly good parts. Pay a gas engineer to do it right a safely
@brotherzaq
@brotherzaq 4 жыл бұрын
Yeah, right, I did, and it cost me 270 quid for new secondary heat exchanger, 50 quid brand NEW off ebay, so basically he charged me probably 200 quid for an hours work - he won't be back, B rip off. No wonder people do it themselves - good for them, just use common sense a know when to get a 'so-called' professional in.
@andrewnewton9891
@andrewnewton9891 3 жыл бұрын
Totally irresponsible. Encouraging none Gas Safe registered work. Why do you think that you have to be Gas Safe registered to work on boilers. Your video could end up killing someone. You need investigating before someone comes unstuck. Shocking.
@MrMeltedwellies
@MrMeltedwellies 3 жыл бұрын
I AM NOT TUCHING THE FRICKEN GAS AT ALL EVER ,INVESTIGATING BY WHO THE BOILER POLICE WHY FOR FIXING MY OWN BOILER thanks for watching Andrew
@andrewnewton9891
@andrewnewton9891 3 жыл бұрын
You are working on a gas appliance. The law says that you must be gas Safe registered even to work on your own appliance. You are in effect encouraging others to do the same. You should ask your self what is the reason of being gas Safe registered ( and no it's not to rip off the public) it's to ensure that people are competent to work on gas appliance so as to ensure safe working practices and not leave the appliance in a dangerous state. This can only be ensured through proper training and education. Which is assessed and recognised by the health and safety executive. Then one can be gas Safe registered ensuring that the criteria for safe working is met.
@jamesknowles550
@jamesknowles550 Ай бұрын
Mark -- take up another part time hobby -- please !
@MrMeltedwellies
@MrMeltedwellies Ай бұрын
Had a new one fitted by company 2 years ago but thank you for all you comments and info
@philmanning2549
@philmanning2549 5 жыл бұрын
completly illigal.
@colinarmour7943
@colinarmour7943 8 жыл бұрын
why are you touching a gas boiler when you clearly don't know what your doing. Anybody watching this don't do anything this guy has done, just pay for somebody competent to sort it
@MrMeltedwellies
@MrMeltedwellies 8 жыл бұрын
+Colin Armour Hi Colin i am touching my boiler that i own and paid for because i have had 3 so called "plumbers" out to look at my boiler and did jack shit and left it not working so i decided to have a go myself,as i have a young child with us and slowly dying of hypothermia something had to be done sorry if this upsets you,and i am also re plumbing my son's house and its been tested and passed by a "qualified plumber" cheers and thanks for watching mark
@colinarmour7943
@colinarmour7943 8 жыл бұрын
You didn't upset me, but I wouldn't put a video on KZbin of something I didn't know anything about, just in case anybody tried to copy and caused damage to themselves or the appliance. Sorry to here that you got shafted by plumbers (they must have been clueless) as by looking at your video if you were getting Hw but no heating then it would have been a diverter valve issue, hope you got it sorted eventually
@MrMeltedwellies
@MrMeltedwellies 8 жыл бұрын
Hi Colin i do have a diverter valve ready to fit sorry to say but i will be filming it lol but i will put a disclaimer telling people not to try this at home cheers mark
@colinarmour7943
@colinarmour7943 8 жыл бұрын
+Mark Davies it's fine to change a diverter valve on your model as it doesn't disturb any gas fitting on your boiler, but when you fitted sensors you would have had to take the combustion chamber cover off to gain access. This should only be done by a competent person. (gas safe engineer) as if the case wasn't refitted correctly or a seal was damaged it could effect combustion and be dangerous. Whenever a gas safe engineer does work that effects combustion he must check appliance with a combustion analyser to make sure everything is OK
@MrMeltedwellies
@MrMeltedwellies 8 жыл бұрын
Ok makes sense my son's mate is a gas fitter so ill get him to pop round and chcek it anyway to be safe, thanks for input will it be ok to use your statment about gas safe engineer on my video
@waleedmakari3588
@waleedmakari3588 6 жыл бұрын
sorry but you go all on the wrong turn , this is not your boiler and it's not your money so if you think you free to kill your self and you say it's your life that's against the low you may face prison sentence for doing that. please think before you act .
@brotherzaq
@brotherzaq 4 жыл бұрын
'course it's his boiler and his money, get back under your rock.
POTTERTON COMBI BOILER 28HE PART 2
2:18
Mark Davies
Рет қаралды 24 М.
How to deal with Low Pressure in a Combi-Boiler
2:52
Ashfield
Рет қаралды 455 М.
Mom had to stand up for the whole family!❤️😍😁
00:39
What's in the clown's bag? #clown #angel #bunnypolice
00:19
超人夫妇
Рет қаралды 27 МЛН
Main Combi 24 HE no hot water
7:25
Annai Illam
Рет қаралды 12 М.
E133 fault Potterton gold 28he faulty spark generator and electrode
14:49
The Mental Gas man
Рет қаралды 12 М.
potterton combi boiler 28he expansion vessel replace
21:27
Mark Davies
Рет қаралды 46 М.
POTTERTON COMBI BOILER 28HE DIVERTER VALVE REPLACE
16:50
Mark Davies
Рет қаралды 75 М.
Why Your Boiler is Losing Pressure and How to Fix It
12:25
Proper DIY
Рет қаралды 138 М.
Кошачья драма 🐈‍⬛🐈 #животные #милыеживотные
0:42
Мир милых животных 🦔
Рет қаралды 7 МЛН
Ouch.. 🤕⚽️
0:25
Celine Dept
Рет қаралды 22 МЛН
Cute - ai mới là người tham lam nhất đây 😝🤪😵‍💫😳
0:16
Nguyên Ngốc Nghếch
Рет қаралды 1,8 МЛН
Эта игра не для слабачков
0:20
MovieLuvsky
Рет қаралды 3,2 МЛН
Jesus tells you the right path to follow #jesus #jesuschrist #jesuslovesyou
0:20