I love the little OLED display, but there's no way that thing complies with 61009. These devices are supposed to be electromechanical and not reliant on a processor deciding when it should operate based on variable software settings. Even with the 'smart' AFDDs from the likes of Hager, the basic overcurrent and earth leakage functions remain dumb and autonomous of the thing's brain so that it can continue to provide those rated functions even if the onboard CPU is borked.
@GadgetUK1644 ай бұрын
Exactly my thoughts! The MCU side should be able to set limits and things that cannot override its standard limits and features.
@jamesbarlow53094 ай бұрын
First thing I thought when I saw this title was to make a "does it have Bluetooth and is it made by Hager" joke. Beaten to it by the man himself.
@mikeselectricstuff4 ай бұрын
I'm fairly sure the Hager AFDD uses the processor for the RCD function - if you look at the instructions it mentions that RCD functionality isn't available while updating.
@Monkeh6164 ай бұрын
RCD functionality hasn't been entirely electromechanical in a long time, especially now we're trying to move away from type AC devices (another black mark... if we believe this thing behaves like a type AC device at all). But there's a big gap between a thoroughly tested firmware (Hager need not apply, mind you) and some generic IoT cack in a knock-off MCU.
@GadgetUK1644 ай бұрын
@@Monkeh616 Yes -that's the key - thoroughly tested, assured - in all aspects.
@bigclivedotcom4 ай бұрын
I've got one here and agree completely. They're a terrible idea. Especially in the hands of the new era of crash certified part-p home automation "experts". It's absolutely guaranteed that someone will remotely turn off all programmed protection on these remotely to avoid having to go and look for an actual fault.
@bigclivedotcom4 ай бұрын
The risk of someone finding this on the hideously insecure Internet of Crap and randomly changing settings is also concerning.
@bigclivedotcom4 ай бұрын
ALSO (rant mode activated) if the power supply fails (as it will) then it becomes a plain MCB of unknown rating.
@reanimationxp4 ай бұрын
@@bigclivedotcom this is the only argument I see as an actual problem with these that isn’t just “we need to keep dumb ppl alive”
@inothome4 ай бұрын
So did you see a way to disable the instantaneous trip coil or the bi-metalic strip in it? From the video I couldn't see anything to override either. So at minimum it should always trip as a C20 breaker. maybe I'll buy one to test. I have seen them in some customers houses, but never bought one to test with.
@Okurka.4 ай бұрын
You're just jealous at someone who has an NICEIC certificate because yours isn't valid anymore.
@noisytim4 ай бұрын
It’s like a piece of conceptual art. “What if safety devices were not only unsafe, but an active safety risk?”
@mikeselectricstuff4 ай бұрын
I do like the idea of filling a board with these and having them switch on & off randomly, or play a tune
@AppliedScience4 ай бұрын
Pretty interesting device! I agree -- seems like it could be improved by having a conventional breaker then adding the computer controlled switch downstream. I've seen WiFi power strips that can control 8 outlets individually, but I don't think they have current/ voltage monitoring.
@elminz4 ай бұрын
My thoughts too. Breakers should always provide a guaranteed minimum level of safety; extra functionality can always be put after a breaker. This device is only optionally safe and safety level isn't easy to ensure. Useful as extra power control functionality in other devices though.
@djtopherau4 ай бұрын
I'm with you ben, I think it has some really good uses cases, but i agree with mike that maybe it should be a different colour,, the RCD function should be a extra and not advertised as such, having said that this defiently should be used in conjuction with a conventional RCD /CBo in series
@inothome4 ай бұрын
Seeing the instantaneous trip coil and bi-metalic strip this breaker should always trip per the C20 trip curve. I didn't see a means to disable that in the tear down. He also didn't test it for the C curve either. C curve fast trip is 5 to 10 times rated for a fast trip. That would be 100A minimum on this breaker. Anything less you have to look at the trip curve. If it doesn't follow the curve then it's just crappy QC, not related to the electronic controls part of it. But appears to always have the C20 functionality enabled. Now the RCD function, yes, that was able to be disabled.
@grant-is4 ай бұрын
The electroboom cut was perfect
@km5lb114 ай бұрын
As an electrician here in the USA this is the worst idea I have ever seen. This should not be allowed anywhere, too much chance for tampering with someone's home, and if it is Wi-Fi it should only indicate the state, not be able to connect or disconnect.
@antoineroquentin22974 ай бұрын
Seeing a circuit breaker turning itself back on is really scary
@Graeme_Lastname4 ай бұрын
I'm thinking about working on tramway overhead wiring and scaring myself. 😱
@hfiennes4 ай бұрын
For the US market, Eaton make an EMCB (energy management circuit breaker) which is also WiFi controlled. However, it has two physical switches - one manual, and one remote controlled. Power only flows if BOTH are on. I have a few of them.
@dalehorton77484 ай бұрын
WHOAH. I couldn't understand the complaints initially, expecting it was an RCD + MCB + WiFi Contactor. When you showed the motor actuated reset my head exploded.
@NoPegs4 ай бұрын
Holy balls, this is even a worse idea than the wifi smart crockpot...
@GudieveNing4 ай бұрын
*crackpot? ;)
@Stealth866514 ай бұрын
I just want a breaker that will tell me over Wifi when it pops, that way I'll know the wifi is down.
@bjornroesbeke4 ай бұрын
And a breaker that turns off when it loses its WiFi connection, just to make the endless loop of dysfunctionality complete.
@DOPPELgameplayVIDEOS4 ай бұрын
My jaw absolutely dropped when I saw the switch physically move itself to the On position remotely.
@relativenormality4 ай бұрын
Right. On the one hand I applaud the PCB design and servo integration but surely whoever designed that would have been smart enough to also think about the consequences.
@kissingfrogs4 ай бұрын
impressive wifi range, zapped Mehdi as far away as Canada.
@Graham_Wideman4 ай бұрын
Hahaha, the slightly wavering wheezy buzz of the motor driving the lever up and down in the final seconds of the video just made me think "Ex-ter-min-ate"!
@eigenvector70354 ай бұрын
I dont know why but the view of a breaker coming up by itself is extremely cursed to me
@prabbit2374 ай бұрын
A wifi breaker that's "report-only" might be a good idea. That way you can monitor things remotely and you could call up the neighbor and say "hey, I'm in Paris. Can you go flip my breaker back on so the aquarium pump will work and I won't have to find another Nemo? Thanks!"
@alancordwell97594 ай бұрын
Its a chilling thought that rather than investigate a potentially dangerous fault that causes repeat tripping, someone will install this so they can just reset it without getting up from the sofa. Fortunately, in most domestic installations, the wifi router will be downstream of the breaker so this won't happen.... Great video Mike, thanks.
@FZs14 ай бұрын
...assuming the WiFi router is on the same circuit as the one that tripped...
@electronash4 ай бұрын
@@FZs1Another very good point. lol Most houses will have just the one router, and it's possible somebody will install it on the same mains circuit as the breaker. So that could lock somebody out from accessing it remotely, which is both good and bad, depending what the settings were on the app last time it was accessed.
@PhilXavierSierraJones4 ай бұрын
You know what this needs? A SERVICE BUTTON. You press it, and it locks the thing out from being turned on or off remotely.
@bobert45224 ай бұрын
Still not safe, not a physical lockout. Can’t trust software or even electrical switching of the motor.
@thomasvnl4 ай бұрын
You know what this product needs? To not exist
@feynthefallen4 ай бұрын
The only thing this needs is a trash can around it.
@Motorman21124 ай бұрын
@@bobert4522 This has so many surprising dangerous features I'm not sure I'd even trust a physical lockout, lest they have implemented a "trip-free" style remote reset on another similar looking model.
@rossthompson16354 ай бұрын
That doesn't address the fact that in operation, the overcurrent or RCD function could have been disabled or set totally inappropriately. Incredible that someone has gone to the trouble to design and manufacture such a sophisticated device, but with no real awareness of fundamental safety principles.
@PowerElectronic4 ай бұрын
The unit has a ton of features. But safety is not one of them.
@cavemaneca4 ай бұрын
I don't think the idea of a Wi-Fi controlled circuit breaker is itself a bad thing, but the implementation here is lacking in a number of ways that make it worse. For one, I would say that the Wi-Fi controlled part should be AFTER the mechanical switch, and should not control the mechanical switch at all. If it trips, or is physically switched off then the Wi-Fi portion sholud not be able to turn it back on. But if it was physically turned on, the Wi-Fi portion can still toggle the downstream circuit on/off, maybe through a SSR or similar.
@tormodhag68244 ай бұрын
It should have two switches yeah, one that reads breaker or lockout and one that says control
@robstamm604 ай бұрын
A circuit breaker which can be configured to NOT break the circuit 😮.
@WizardTim4 ай бұрын
Wow... This is exactly why devices have warnings on them like "AUTOMATIC START" and "EQUIPMENT CONTROLLED REMOTELY", the only hint you get something is up with it is that OLED, but those circuit breaker characteristic markings would entirely have mislead me into thinking it's a normal RCBO with an OLED readout. It has so many risky failure modes but I would be particularly worried about the software glitching or getting hacked, Mr Robot plot line idea there, blow up the building by re-configuring their circuit breakers... Also interestingly it's marked as only a Type AC RCD, considering there's an entire WiFi connected computer inside which measures the current I don't see why they couldn't get Type A or even try to get Type B with a little more circuitry? Even more so for arc fault detection? Looks like it already has all the needed circuity for that functionality, just needs software for it.
@JohnEdwa4 ай бұрын
I've seen breakers like these used basically as just switches/disconnectors for EV chargers, solar inverters and other gear like that, and for those applications it could be useful. But I agree, the form factor is an enormous risk. At least it should have "NOT A BREAKER" plastered in big bold letters on it.
@inothome4 ай бұрын
How is it not a breaker? It has the magnetic trip coil for instantaneous and bi-metalic strip for over current that can't be overridden. So at minimum it should always be a C20 breaker. Yeah, the RCD can be disabled, but not the over current.
@tschuuuls4864 ай бұрын
@@inothome because it has the ability to turn itself back on!
@JohnEdwa4 ай бұрын
@@inothome The overcurrent can also be disabled, showcased at @ 7:45.
@inothome4 ай бұрын
@@JohnEdwa He didn't test it correctly. A C curve breaker at 2.5 times rated current (50A for 20A breaker) the trip time is 40 to 55 seconds. He only let it go 10 seconds or so. Look up the C curve trip chart, that will explain it.
@apehat4 ай бұрын
I guess the good news / bad news is that within a couple of years the app will no longer work, or else you have to enroll in a subscription service to powet your lights.
@davelowe19774 ай бұрын
The starting point for this design was a 21 year old with a copy of Android Studio and a flat with a faulty mains installation.
@hikariyouk4 ай бұрын
Turning off, kind of cool, I guess. Turning it back on remotely...oh dear god, that's just the worst idea possible.
@charlesdeens89274 ай бұрын
One thing the manufacture could do to make it a bit safer, is design it so it can detect when the breaker is manually turned off. If manually turned off, the app will not be able to turn the breaker back on and the breaker can only be turned back on manually.
@TestGearJunkie.4 ай бұрын
Thing is, the manufacturer doesn't care if it's safe or not.
@gaeel3304 ай бұрын
Starting this video, this seemed like a good idea to me. Being able to remotely cut power in the case of a fire or other safety or security issue seems like something useful. I didn't realise that it could also turn back ON, what???? There's absolutely no way that a circuit breaker should be able to turn back on without someone physically manipulate it, and I'd be surprised that this is even level to install in most jurisdictions. That's absurdly dangerous!
@jacekowski4 ай бұрын
Actually, tripping curve for C type breaker at 2.5x nominal current allows for trip times up to around 30-40s.
@techcafe04 ай бұрын
that's one ridiculously over-engineered circuit breaker. and dangerous.
@watsisbuttndo8294 ай бұрын
Letting the ccp have control of your power panel couldnt possibly have any ramifications.
@Eng3nhoc4s4 ай бұрын
Social score -1000000 xD
@luminousfractal4204 ай бұрын
Yeah china china. Our ones are just as bad but can rule your life all the more. China is the safer alternative being half blocked in the west 😂 big clive did a great teardown on uk smart meters and how dodgy those are.
@PEK-974 ай бұрын
@@luminousfractal420 Exactly. China makes high quality electronics at a decent price. Hate it when ppl whine about something being a piece of crap when they are the ones paying a fraction of the price😂
@tin20014 ай бұрын
@@PEK-97 It's not the quality of the electronics that are a concern. It's the software. I am quite enjoying finding ways to make my life easier through smart devices... But there's no way on Earth I'm going to be letting China, or even America have control over my stuff. I won't use anything I can't reflash with Tasmota or ESPHome and know it's mine. It's a security risk.... And entirely ridiculous to need a server in another country to decide whether my light should switch on or not.
@docpaul4 ай бұрын
Good to see you back Mike, and a shout-out to Artisan Electrics - nice one mate!
@TheRasteri4 ай бұрын
It's like a parody of IoT that somehow made it to production.
@UnbeltedSundew4 ай бұрын
Maybe, despite it being built to look exactly like a circuit breaker and to fit in a breaker box, it's meant to be used downstream of an actual circuit breaker. Could be very useful for certain things, for instance like having it on a timer for garden circuits or outside outlets.
@reanimationxp4 ай бұрын
there’s tons of devices like that on the market, they’re all over Amazon for $5. this one is specifically intended to be a remotely switchable circuit breaker and power monitor
@UnbeltedSundew4 ай бұрын
@@reanimationxp Oh, I'm sure there are. But I doubt they have the advantage of being as confusing and as dangerous and so easily open to misuse. I'm not sure why this thing was created when all those other options for somthing downstream in the line exist. To my mind it's definitely meant to replace a circuit breaker.
@ElectraFlarefire4 ай бұрын
I'm with others.. Label it 32/50A whatever and 100mA RCD trip.. And make it so the electronics can ONLY turn it off/trip. Then it seems like a good idea.
@paulmoir44524 ай бұрын
That and rewrite a bunch of lockout-tagout regulations... EDIT: Nevermind: reading comprehension fail.
@michaelmoorrees35854 ай бұрын
Designed to be remotely turned on, because the designer saw the first Jurassic Park movie, and didn't want to suffer the fate of Samuel L. Jackson's character. Standards and safety, be damned !
@dimitar4y4 ай бұрын
HAH the use of mehdi here was perfect.
@witeshade4 ай бұрын
Wait. So if there's a lightning strike and the cpu gets scrambled and locks up, or there's a software bug, it completely loses all overcurrent and circuit protection?! So one day your water kettle shorts out and this thing just lets it dump power until something catches fire?
@witeshade4 ай бұрын
Ah I just kept watching. It has the thermal and coil protection at least. That's something I guess!
@user-gx1rk8yw6l4 ай бұрын
@@witeshade But it will not trip if at the wrong time it is being updated...
@ridefast04 ай бұрын
Interesting! So - if your router power goes off, you won't have WiFi to turn it back on!
@georgesnow4 ай бұрын
People that invested in smart homes would have a ups on their wifi router
@TestGearJunkie.4 ай бұрын
@@georgesnow Or not use wifi at all. Don't think it's ever been enabled on my router. There is a UPS on the main network rack though, which the router is powered from.
@riccardoiacob45604 ай бұрын
I would just use it only downstream of a "real" RCBO, it would prove useful in situations where you want to monitor the power and/or do priority-based overpower trip.
@PEK-974 ай бұрын
Watching your demonstration of this product gave me an idea to improve its safety: They could manufacture the breaker switch to have 3 positions: ON OFF and TRIP (from top to bottom). When it trips due to overcurrent or earth leakage, the switch snaps from the ON position to TRIP. When it's controlled through software, the switch only travels between ON and OFF. The design would only allow the motor to mechanically drive the switch ON or OFF but never when it's in TRIP. This would be good for two reasons: - A breaker trip due to some electrical fault will always require a manual reset, not possible to do remotely. - If an electrician needs to work on the circuits, s/he can pull the switch to TRIP, disallowing any remote control. Anyone knows if such type of RCBO already exist in the market?
@HenryLoenwind4 ай бұрын
Any RCBO combined with any rail-mounted wifi switch.
@BenMitro4 ай бұрын
No one stopped and asked "What's the purpose of this circuit breaker?"
@christopherstaples67584 ай бұрын
well I use them for data logging , but now having seconds thoughts with the software overrides without a manual lockout , plus out septic pump trips all the time when it rains
@BenMitro4 ай бұрын
@@christopherstaples6758 I can see some uses too. My point was at the design phase, they forgot its primary purpose.
@user-gx1rk8yw6l4 ай бұрын
Being able to REMOTELY turn off the basic function of a circuit breaker makes life super-easy for John Arsonist... 😞
@Buugipopuu4 ай бұрын
The march of technology means that now you don't have to worry about ransomware encrypting your family photos, but ransomware burning your house down.
@user-gx1rk8yw6l4 ай бұрын
@@Buugipopuu Yeah... [sigh...]😞
@bagofholding4 ай бұрын
As long as the wifi router is downstream of this breaker and not on a UPS...you might be safe.
@asdfasdfasdfasdeff4 ай бұрын
Wow. Conflicted. The Home automation dork in me loves this but the electrician in me hates it. This is supposed to be a basic safety device, not a power switch.
@user-cr4sc1ht9t4 ай бұрын
There are Wi-Fi power taps that goes in between wall sockets and fire hazards, that's still a bit stupid but significantly less so than Wi-Fi enabled circuit breakers
@dimitar4y4 ай бұрын
but if it turns off the power to the router, how will it wifi?
@sanches24 ай бұрын
Soo here's the intrinsinc safety feature - it locks itself off:))
@TomStorey964 ай бұрын
Stop thinking logically. Think of the convenience of turning stuff off from the couch or while you're on the John!
@lexicase88054 ай бұрын
11:14 As with most tuya devices, you can open the screen where the bar graphs and power displays are in the app, the picture of pen and paper up the top right is for renaming the device as you wish
@dmatospt4 ай бұрын
Critical security functions implemented in low-quality software? Yay! Could be useful but only in addition to the real thing upstream.
@arcadeuk4 ай бұрын
I love that once the WonHungLo capacitor dries up and gets into a loosing battle with the grid, this "circuit breaker" turns into a pass-thru device 🤣
@ncot_tech4 ай бұрын
Don't worry... it's got a CE mark on it, all is well. It'll fail safely. 🤣
@DeakBrenan4 ай бұрын
Maybe the 485 port is for daisy chaining them with link cables in the recess so they can negotiate their IDs for the app to identify them correctly? IDs like Mental01, Mental02 etc.
@keithmarlow1434 ай бұрын
It’s an EFD, electrician frying device
@kurosumomo4 ай бұрын
Don't you have main fuses? Here every house has main fuses, you take them out before you do any major electrician work. For multi apartment buildings, the main fuses for each apartment are separate and only accessible to the electrician, next to the electricity counters. So you pop those out after inspection and get to work. While this thing seems rather pointless, I don't think any electrician worth a damn would get "tricked" by this.
@JohnD-JohnD4 ай бұрын
I looked these up. I don't see these being intended for main panels. These are din mounted breakers that need a wire for the hot instead of tapping into a bar behind the breaker. The main purpose of these would be for building enclosures downstream from the main panel for things like controls or remote monitoring of devices. Good example would be lighting control system, but there are many other useful applications for things like this. Controls, EMS, monitoring, timers, etc.. I would not hesitate to build something like this into an external enclosure that needs to be monitored for power consumption because it would save the need for additional equipment like CT's and a separate energy monitor. Between the Zigbee and WiFi connectivity options, it gives a lot of flexibility in how to integrate it into an application as well and saves the need to run ethernet cables or installing cellular modems to connect to those enclosures. Overall, I like the idea behind this device, there are a LOT of uses for it.. just not in a main panel.
@ferrumignis4 ай бұрын
This isn't a typical UK single circuit RCBO unit which has a single live at the bottom for a bus bar, but it does have the same connections as an RCD in UK consumer units which protect multiple different circuits so could easily replace one of those.
@EyeMWing4 ай бұрын
Yeah, pretty much. The difficulty is that some UK-type residential panels *are* just DIN rail enclosures, and are wired this way. A very specifically British problem for their very specifically insane way of doing things. It's no wonder they're so terrified of electricity that their plugs are absolute fortresses - the way they wire their buildings is just madness.
@Jdbye4 ай бұрын
Connected in series with a normal breaker, this could be a useful device. Even in that use case, it needs clear labeling, so people know to turn off the parent breaker when they need to work on something. Ideally, this should not be in a breaker form factor at all, so as to discourage installing it in a breaker box or treating it like a standard breaker. If it could only be installed externally, more like a light switch or smart socket with safety features, it would solve most of the safety concerns, and used like that to protect specific parts of a circuit it could be quite useful.
@ShortFilmVD4 ай бұрын
If it ever started tripping, you'd be second guessing whether there's an actual circuit fault, a breaker fault or a WiFi/app fault, I'd personally rather invest in 'Smart Switches' if I needed remote off-on functionality. Remote circuit reset just seems wrong, if you think you need it then you've probably got a design flaw in your circuit, expecting tripping ins't good.
@sorphin3 ай бұрын
the appearance of Mehdi getting zapped just sells it.. lol
@Evbmw4 ай бұрын
Back in the day : Fuse blows, fit thicker fuse wire. Today : These's an app for that!
@TheWebstaff4 ай бұрын
Yeap and that can be a good thing. If the normal.load is less than the default rating you can turn it down a bit so it's safer. Just make sure to fit a good breaker upstream of this and label appropriately.
@JanicekTrnecka4 ай бұрын
Remote controlled relay or contactor...ok, but resettable circuit breaker nope nope nope.
@greerbriggs84214 ай бұрын
holy moly, who would ever think a safety device *where you can turn off the safety* would be something sane!?
@OmgSaySomething4 ай бұрын
It gives the owner an -option- to turn off features they don't want. Nothing wrong with that. You can turn off ABS on your car too.
@2009dudeman4 ай бұрын
@@OmgSaySomething Traction control most cars let you control with a manufacturer installed button in compliance with safety regulations. ABS they don't intend for you to disable, hence there being no "ABS Off" button on the dash like you do for traction control. No, unplugging wheel speed sensors doesn't count, as that would be like installing a jumper wire from the bus bar to the breaker output lug and acting like thats intended to disable features you don't want.
@mechadeka4 ай бұрын
@@OmgSaySomething Having a working circuit breaker isn't a "feature".
@OmgSaySomething4 ай бұрын
@@2009dudeman Okay, ABS was not a good example (albeit one can pull its fuse) but the other "driving aides" can be turned on and off. In this case, there are functions of this thing that the owner can decide to use or not. It is not wrong. It being motor driven, is fundamentally wrong; if it's a common breaker that can be armed or tripped remotely would be better. Of course, then one couldn't set its tripping parameters.. As someone wrote this thing could be absolutely useful as a secondary safety device in series with a primary one.
@OmgSaySomething4 ай бұрын
@@mechadeka One can trurn off some of its functions. Like, they want the over and under voltage function but not the ground fault protection, what is wrong with that? As someone wrote this thing could be absolutely useful as a secondary safety device in series with a primary one.
@RocketCityTech4 ай бұрын
When you turn off the power to the circuit your WiFi router is connected to… 😂🤣 Doh!
@electronash4 ай бұрын
Wait, what? Are you saying that if you disable the current limit in the app, it will pass 50 Amps or more, without tripping OFF at all? :o So many things wrong with this. I get that there is a market nowadays for "smart" control of mains devices, but there are too many things wrong with this design.
@electronash4 ай бұрын
7:50 - That's SO bad. lol So it really is controlled by firmware in the breaker? Presumably the app doesn't need to be running in the background for the OVP and current limits to work, at least? The fact that you can *disable* the current limit in the app, and the RCBO won't trip with 50 Amps or more through it, means it's no longer a circuit breaker at all. :o To me, that's the single most dangerous part about this. It should be combined with a "physical" 20A breaker (or whatever the rating is) internally, that can *never* be overridden.
@TD-er4 ай бұрын
It is a C20, thus C-characteristic (not sure if that's the same term in English, in Dutch we call it C-karakteristiek) Meaning that in the range of 8x (+/-20%) the nominal current it should react within 2 - 3 seconds At lower (less than 4x) multiples of the nominal current it doesn't matter whether you have B/C/D characteristic. At roughly 2x nominal you can draw such currents opto 70 sec until it pops. (regardless whether it is A/B/C char..) Well this is assuming the device is really operating according to specs. N.B. Power trips with B-characteristic should trip immediately when drawing > 4x (+/- 20%) of nominal rated current. I wonder what kind of WiFi microcontroller is installed. Judging by the form factor it could be an ESP12-F like device which makes it even more dangerous as people will start experimenting with overriding the already few protection measures present.
@youtubasoarus4 ай бұрын
Yep. He showed it not tripping at 55A+ 😬
@electronash4 ай бұрын
@@TD-er Yep, it looked like an ESP style module. I know some others can look very similar, but it was very close to an ESP8266 shape. And yep, the C20 would have some tolerance as well, and a certain time to trip. But the scary thing is, this isn't really a "breaker" at all, as it has no mechanical breaker for that trip current, and can be overridden. Such a dangerous idea. lol
@electronash4 ай бұрын
Oh, also the fact that it's relying on the motor driver, motor, and gears, to "trip". I would trust an older mechanical breaker (with RCD) any day over a yet another badly-designed IoT device.
@retrozmachine11894 ай бұрын
Motorised over current trip by the whirring sound. That has to be the worst possible way to do it. Why wouldn't they do it with a plunger/coil or coil/magnet approach? Much more reliable. It won't trip without both phase and neutral present too, I'm guessing.
@SeanBZA4 ай бұрын
Has an actual current trip and thermal protection, though I guess to trip on thermal you need 60A of current flow for 30 seconds, standard trip time for thermal breakers when cold, and for instantaneous trip you need 100A for a half second to do the magnetic trip. Thicker wire through that toroid, like 10mm cable 5 turns, would probably have gotten a trip out of it with no power applied to the breaker.
@retrozmachine11894 ай бұрын
@@SeanBZA Yes, I saw that later on, but it definitely appears to be far in excess of the 20A rating so the motor doing the trip for the supposed rating is rubbish in my opinion.
@SeanBZA4 ай бұрын
@@retrozmachine1189 The trip mech is standard for all breakers, so it does meet type approval. The biggest issue is the RCD that can be programmed off, which is a big issue for a breaker that shows as a ground fault protection device at first glance. Should have had an automatic 100mA trip built in, not removeable with software, and running direct to the trip coil itself to trip on a major ground fault.
@retrozmachine11894 ай бұрын
@@SeanBZA It says C20 but that only appears possible with the action of the motor, not the thermal strip. That should make it fail approval in my opinion. Magentic trip may well be appropriate for C20 rating.
@mikeselectricstuff4 ай бұрын
@@SeanBZA The approval claimed is for the RCD functionality. I also don't believe the C20 rating
@francistheodorecatte4 ай бұрын
well, the good news is that uses a Tuya Beken module for the wireless control (the one marked WB3S), so running your own firmware on this wouldn't be too hard thanks to OpenBKT.
@benjaminsmith36254 ай бұрын
I'm always amazed by the miniaturisation in these DIN rail devices!
@MINKIN24 ай бұрын
"Hello, Support? My RCD is not working..." "Have you tried turning it off and on again?"
@mogoreanu4 ай бұрын
I enjoy Mike's "lovely" when the breaker turns itself back ON you after the voltage returns back to normal. Lovely indeed, one might even say Lively.
@NotSexualAtAll4 ай бұрын
so.. in RCD failure, it _snaps_ right off, and in overcurrent failure, it uses it's internal motor to turn off? wow. how did this get certified for sale?
@inothome4 ай бұрын
For short circuit it still has the magnetic trip. For a few times OC you don't need instantaneous, since that usually is a bi-metalic strip anyway. Which this also has more than likely to meet the C class 20A rating.
@robertbackhaus89114 ай бұрын
For gross over-currents, there is the mechanical breaker - fast-acting magnetic one, slow acting thermal one. For less than that, there is the micro-controller driven current sensing. Strange that they have the fast-trip mechanism for the RCD, but don't use it from uC-detected overcurrents.
@web1bastler4 ай бұрын
Most likely it has no certificates at all. It's pure chinesium and in china people don't care about safety.
@ejonesss4 ай бұрын
not only a shock hazard but a hacker could shut off your power
@thisnthat35304 ай бұрын
Does it store enough energy to trip with no power being supplied? A dead short could reduce the effective supply voltage to near zero.
@marcootto924 ай бұрын
bye bye fire insurance....
@rbland4 ай бұрын
Are these even legal over there? The tripping characteristics are super dangerous. I don't think this follows a 'C curve' MCB at all. 50 amps and a few seconds to trip looks very wrong to me
@laughingoreilly13344 ай бұрын
The more complicated it is the more likely it will go wrong
@thomasesr4 ай бұрын
It's only dangerous if it's installed by itself, I would put it after a real dumb thermal circuit breaker in series. So anytime I need to do maintenance I would switch off the dumb one.
@martin090919894 ай бұрын
Here in Germany we have the 5 safety rules. One of them is "secure for turning back on" in case of a circuit breakers this means stick a wire through the hole in the lever like it's intended to! An this one hase that feature clearly visible, and the mechanism works the right way. But shutting off or altering the values (in the wrong direction) of the safety features i clear no go!
@christopherstaples67584 ай бұрын
good points mentioned , I did not think about a lockout ,geez over 50Amps and still not flipping also they have voice activated version as well
@cnvogel4 ай бұрын
Should be noted that there are, in fact, products combining the functionality of overcurrent and residual current protection and remote control on the market (eg Schneider Reflex iC60 & you clip on an additional RC/GFI). And they explicitly address all the safety issues, eg you have a lockable lever for lockout, they mention all the failure modes in the manual… but of course they are €500, without wifi (being professional gear, they are controlled via individual wires with control voltages)… on the other hand, nothing prohibits anyone adding the safety features to a wifi product, does it?
@ruben_balea4 ай бұрын
Even with the same construction they could just remove the external part of the lever and cap the holes and it will be like a timer or any other mechanism you won't rely on to cut the power before working on the circuit.
@thecombatengineer70694 ай бұрын
I believe this is a hackers dreams.
@reanimationxp4 ай бұрын
Turning off power to one room in your house is a hacker’s dream? Hardly. Your Smart TV signed into Netflix would be a lot more useful to pivot from.
@youtubasoarus4 ай бұрын
Every new IoT device in peoples houses is already a hackers dreams.
@JonathanSwiftUK4 ай бұрын
You do have to be careful with automation. The other day we had a power cut, South London area, it is very rare, apparently a cable fault. Anyway, the power came back on, I went into the bedroom, and I could hear this clicking sound, about once per second. I tracked it down to a new TP-link Kasa smart plug. Luckily there nothing plugged in, but it was bust. Tried resetting it, no joy, I plug it in and it keeps clicking on and off, if I press the override power on/off button a bunch of times I can get it to stop, but when I plugged and plugged in the whole thing starts again. Imagine if I had a dehumidifier or computer or some motor on there. It has made me think twice.
@WizardTim4 ай бұрын
Those Kasa smart plugs are complete garbage. I had to deal with them back in I think 2018? They would always be crashing, losing WiFi and then get stuck quickly switching on and off forever, lucky they were only ever used for lights. Customer support knew it was an issue and sent free replacements with a different hardware revision, they worked better but still died after a few months with the same on-off fault, if I remember correctly they have a capacitive dropper PSU which degrades very quickly because they run so hot, after a few months baking it just browns itself out every time it tries to turn on the WiFi radio or close the relay.
@Bigrignohio4 ай бұрын
Seriously, if people want this sort of control send the circuit through a separate control line-voltage contactor.
@TheWebstaff4 ай бұрын
Yeap we just put another fuse box above and run from a good rcbo into these. 🤷 I have one in my garage to control the power circuits. I walk out the garage and the beacon detector knows to power down everything.
@Berkeloid04 ай бұрын
Absolutely, and control it via RS485 or similar, not some dodgy WiFi chip that can be easily hacked into and controlled by someone sitting in their car out in the street.
@TornTech14 ай бұрын
I wonder how well that wifi antenna works in the new compliance entirely metal consumer units?
@mikeselectricstuff4 ай бұрын
Good point - not well I suspect
@TheRasteri4 ай бұрын
@@mikeselectricstuff I suppose that's why it needs the RS485 upsell option
@braelinmichelus4 ай бұрын
I can see value in some of the features in it, however, you wouldn't want them integrated into what should be a life safety device. The voltage and current monitoring is cool, but easily could be done with a module external to the consumer unit that has proper mains isolation as well as being ancillary to an actual RCBO. However, I don't see why would want a remotely-switchable breaker. Switches suit the purpose just fine. Should note I'm specifically talking about the average homeowners or DIY dads here, and not electricians or contractors. And they should know better than to use one on their own accord. It's truly horrifying to think about the situations people that know no better would put these into.
@user-cq8vn1he9t4 ай бұрын
completely agree with you. as you say there are uses. i saw these a while back when doing an energy saving project at work. i wanted to isolate a whole ring final circuit due to out of hours wasted consumption. i ended up using a normal smart switch and a contactor. this device is basically that with the extra functions of energy monitoring and adjustable trip characteristics. so yeah, its really really cool actually, but it needs to be fitted in addition to normal protection. also, not look like a breaker. not claim to be anything like that. obviously, also, be manufactured to an actual standard haha
@somethingsomething4044 ай бұрын
Wow that’s strange. At first I assumed it would be for turning wifi on and off
@ikocheratcr4 ай бұрын
I can only think of this as a prank device, or a 'nothing to see here' network backdoor device. Looks innocente enough, and can provide lots of "interesting functionality".
@gautamdamodaran4 ай бұрын
This thing shouldn't have a place in any electrical distribution box. The rcbo/rccb etc. are made simple for a purpose.
@cmjones014 ай бұрын
I wonder what its breaking capacity is? What would happen in the event of a 5000A fault? It doesn't look like there's a lot of room left in there for arc quenching...
@mikeselectricstuff4 ай бұрын
The breaker side looks fairly normal, so likely smilar to a standalone RCBO
@MarkGovier4 ай бұрын
Quite neat. I can understand the concern about the ratings on the device. Now, here’s a tip for the manufacturer; use an E-Ink display and have the prevailing ratings shown on the screen rather than printing like a standard breaker. Otherwise, there are definitely uses for auto-re losing breakers that have been around for a long time. As the “switch” part of the design is fairly standard and it can be “locked off” there is little trouble in my mind. Warning labels on the cabinet should also be applied “Part of this installation is fed via an automatic circuit breaker, position CBX.XX, ensure that the power source is isolated or that this device is locked off before working on XXXXX”
@gunnargu4 ай бұрын
I'd love one that JUST measures energy usage, but does not have the _capability_ to control the power.
@TheWebstaff4 ай бұрын
Just fit it after a proper rcbo that how we use them in an external din box. I did discuss with our spark about stacking them in a double din setup but we decided because it's not checked by the fuse box maker it wouldn't be compliant so we ran them out of the fuse box to avoid the issue. Then labeled accordingly.
@meeder784 ай бұрын
Shelly has those kinds of devices.
@hfvhf9874 ай бұрын
Blimey, you should have saved this episode for Halloween, it's that scary!
@decryptic9994 ай бұрын
Everything seems solid and really nice, except one thing... the on feature. As an Automation Engineer, I work a lot with Fuses, Machines and Coding. If a Fuse is taken out, either by us to repair something or because we have something wrong, I don't want that ANYONE can turn it on again remotely. Also the Timer is horrible! Imagine it turn off and you look at it and now you have to find the problem. Or it is already turned off and you think it is save, until it automatically turn it on again... My solution: Get rid of the Auto- & Remote on feature. Done! Product is 100 times more safe. Second: If you need to turn things on or off, get a remote Relays. This thing is designed to turn on and off. So when you want to be save, Trigger the Fuse and you're save (to a certain point, of course).
@cods414 ай бұрын
Thats pretty clever. Amazing they can fit all that functionality in there. It has most of the same functions that a pretty advanced MCCB or even a high voltage circuit breaker has. It definitely needs some clear signage in the panel saying it is remote controlled, and a local/remote switch to disable it.
@TheWebstaff4 ай бұрын
We have used quite a few of these for car chargers at the old office I worked at. When we used them we put them behind another rcbo in another din box, so we got best of both worlds. Reliability of a known breaker and the smart features of these. Been in use for 3 years now?. (Older version) Never been issue with them. 🤷🤷 Totally agree they are non compliant. I mean tuya or the OEM who made them don't make fuse boxes for them for a start.. that alone should set of alarm bells for any sparky. But yeah we have a big label on them please use rcbo for isolation. We did have fun when our spark turned up though he though he was putting these into the main fuse board. We all had a good giggle and then showed him the other din box to house them in.
@TheResistorNetwork4 ай бұрын
When I saw the thumbnail, I knew this was going to be a good one!
@sandervesik1734 ай бұрын
So to be a reasonable device you would actually want to anywhere around you it would need to: a) drop the motor function b) make the residual current and max current functions be good old hardware c) reimplement all the other functions as software triggering a test button press on the breaker completely different device. But would at least not be dangerous while still retaining most.
@aminalwashe32974 ай бұрын
They should use a separate relay after the breaker and everything should be fine, right?
@TheWebstaff4 ай бұрын
That's how I've always had them wired up after a certified fuse board with appropriate rcbo's.
@Berkeloid04 ай бұрын
The point in the video was that they look too much like normal circuit breakers, which can be relied upon not to switch themselves back on when you're working on the circuit. They'd have to change its appearance to make it look like a different kind of device to avoid that problem. Then there's just the issue of the labels specifying it as a 20 amp breaker and 30 mA RCD, when both those values can be changed or turned off completely, making the labels incorrect. If you could make the labels match the current config and make it look less like a breaker then there would be much less chance of a dangerous mistake being made by someone unfamiliar with the electrical installation.
@GadgetUK1644 ай бұрын
Very interesting video Mike!!! I think the main thing that would put me off here is the fact all of that functionallity is controlled by an MCU, with seemingly no "common sense" hardware to override in relation to safety. eg. at the point you managed to draw 50A through it - that shouldnt be possible. I would fear what kind of bugs exist in the firmware for that device, and what happens when the MCU locks up / dies / does something you dont expect... And - lets face it, what kind of reliability could we expect on the MCU and power circuit for that MCU and OLED screen - I bet after a few years that MCU or the PSU capacitors will go pear shaped... I think just the idea of having that control PCB inside an RCD scares the hell out of me lol
@rocketman221projects4 ай бұрын
It would be nice to have the monitoring functions from this in a breaker from a trusted manufacturer, but with RS-485 or CAN instead of WiFi.
@landonbrown52954 ай бұрын
There was mention of RS485, but it was an addon module
@peterknudsentupni4 ай бұрын
Several years ago I worked at an electricity supply company. breakers with that functionality were quite common on a large scale both on high voltage and 400v. If the small din35 version gets a little better so that security can be locked to what the branches can load at most, it will be really good.
@szabolcsmate52542 ай бұрын
This would be a fantastic product! If it didn't - very convincingly - pretend to be a circuit breaker.
@Electronics-Rocks4 ай бұрын
The main issues are needs to be labelled correctly & the internal thermal overload needs to be lowered otherwise a useful device but i would put downstream of conventional protection supplied from a recognised source!