I’m so glad that you are posting again on a regular basis. Keep it up!
@smoguli11 ай бұрын
You should never use an outlet at 100% of it’s capacity over long periods of time. A regular household outlet in a house can output 15A over short periods only (we’re talking minutes here). For longer periods (hours), you should never exceed 80% of the outlet’s rating. That’s why Hyundai’s level 1 charger tops out at 12A, because that’s 80% of 15A. If the wiring in your house is old or too thin (small gauge) it could overheat and cause a house fire.
@jeremyrom11 ай бұрын
I totally agree! The product that this video sponsors may be dangerous to some people. 12A is a much safer limit for basic level 1.
@dh203211 ай бұрын
if it's ring main, I.E. the power go to ways, round homes ring main, 15A but as the power going in the two directions at the same time 15A one and 15A going the different direction way = 30A, but that's assuming a lot, the the plug socket was installed to the highest of standards? and not botched job from the start? and even if it was connected the ring main, one side may of failed, and socket drops back to, 15A, and without never knowing running only 15A, is going to be fire hazard in you wall spaces or wherever cablesare going to and from the socket? so yes, the power socket not expecting and in the case the wall look like wood?
@smoguli11 ай бұрын
@@dh2032 ring main is used in the UK, we don’t have that in North America. But your point is still valid, in an older house it’s very hard to know if the wiring and outlets are of good quality and correctly installed. It’s also common to have multiple outlets and fixtures that share one 15A breaker.
@daveo919811 ай бұрын
The Lectron EVSE at 15A would be ok on the NEMA 20A plug, with the 80% rule, but the plug tip should be permanantly horizontal to prevent it from being used in a 15A circuit, and overheating. Also dont forget there are likely other devices on a standard 15A circuit that draw current.... If Solomon is only able to use Level 1 because his home is a rental, and the landlord is unwilling to add a 240V plug, there is a device that links 2 120V branches on different phases to output 240V. That might be a solution for him, else a dryer plug adapter might be useful....
@vulpixelful7 ай бұрын
@@daveo9198The 15A plug should not have the horizontal tip because standard outlets in the US are rated to 20A, and it isn't against code to have the regular three pronged outlets for both 15A and 20A currents. The only way to be sure about which one you have is to check your breaker box.
@muskrat329111 ай бұрын
I also have a Kona EV and I only have level 1 charging at home. Since I no longer commute on a daily basis, level 1 works great. I wait until my SOC is in the 30% to 40% range before charging, usually about once per week using the EVSE that came the car. Also, the car is set to charge only during off-peak utility rates.
@AlainODea11 ай бұрын
Thank you Solomon. This is great information and good guidance on the trade offs of different charging (EVSE) options.
@1hjehje11 ай бұрын
This video is really informative, Thank You! I think that it would be an excellent introduction to EV charging, especially for EV newbies. This should be common knowledge, but it is not good practice to run a charging cable across a sidewalk or walkway as it creates a tripping hazard. If a business is willing to provide outlets for the purposes of charging an EV, or for plugging in block heaters which is common here in Canada, they should consider installing charging posts. This is sometimes problematic as motorists often damage them when they are covered with snow, etc.
@IgneusDarkSide11 ай бұрын
This was both insightful and helpful. Delivered in such a nice and composed manner.
@daveromanyshyn117015 күн бұрын
I tried to go with level one only when I moved for my F-150 lightning. I had a shorter commute. It worked most of the time but if I had a day where I drove a lot, I was not able to charge fast enough. Luckily I have a Tesla charger in all directions that I travel so I could use those in emergencies. In the end I had a level 2 charger installed which I am glad I did.
@scratchymaster11 ай бұрын
Wanted to add that NEMA 5-20 outlets are supplied by 12gauge wire and get a 20 amp breaker. Some households might already have 12ga & 20 amp breaker, but not the NEMA 5-20 outlet.
@arlyn821111 ай бұрын
This is great! Love the detailed information about the pros and cons!
@BensEcoAdvntr11 ай бұрын
Great video; Level 1 charging works for a ton of people. So many reviews and articles just parrot the notion that L1 is so slow and therefore useless. I have L2 now for my Chevrolet Bolt EUV but only because GM paid for a NEMA 14-50 outlet. Previously I got by just fine on L1 for my Ford Focus Electric since I rarely drive more than 30 miles per day
@shaunmckenna192311 ай бұрын
Hello Solomon I just found your winter drive video from way back, great info as I do drive from Vancouver Island to Calgary I have a GV 60 so I am always interested in new tips. I have learnt 2 good tips this video for me while travelling one I will carry an heavy extension cord two a charging cable wheel protector , as you said most motels / hotels have outside plugs , I think it would also be a good idea to have some type of flashing LED light to mark the cord over a walkway from the plug to your room so people would not trip. Thank you for a great video look forward to more .
@vr28079 ай бұрын
Fantastic Video, I Understood Everything. You Gave A Reason to the EV Charging Madness! Thank You!
@DaveKCMO-u6n6 ай бұрын
Thank you! I am getting a PHEV soon and this video was quite informative and helpful!
@neygercey78995 ай бұрын
Many thanks for all those very useful information and tips.
@user-ff8ju1ee9b11 ай бұрын
Keep making these good videos.
@diydrivenGA5 ай бұрын
Another note: for battery life longevity, it has been shown that many shorter and smaller charge sessions is better than a few long and fast ones. Also storing your car in hot climates or garages with more than 80% is detrimental as well. Meanwhile dropping below 20% is a recipe for getting stranded if you leave it parked for a few days. Sweet spot is to keep the car between 40-80%. Given you can get 10%-15% overnight means you can totally get by on mostly level 1 charging and use a supercharger occassionally when there is road trip or a long day of driving. Charge where ever and whenever you can if going on trips.
@Truth1000.4 ай бұрын
thank you, very helpful, many miles to you on your journey
@diydrivenGA4 ай бұрын
So watching this again and wanted to share some of my experiences as I have been using lv1 for a month or so and will be adding a dedicated 240 outlet for level 2 charging at home. Regardless of if you are staying level 1 or want to add an outlet for level 2, You will want to install a dedicated circuit for it to make prevent issues with an outlet on a circuit and to make sure you are safely charging. I am in the process of recording a video that details my story as I think it is something that will be helpful to others and isn't something I've found online as of yet.
@southerncharmsssy2 ай бұрын
I use Level 1 every day and have had no issues with my 2024. Excellent video btw...I watched this in its entirety😊thats a first for me!
@jimwheler150111 ай бұрын
Nicely done
@astronaut527 ай бұрын
Great information. Thank you.
@edlizard11 ай бұрын
And with more efficient EVs like the Aptera (if they can even start building them) Level 1 Charging may be good for 99% of everyday use.
@jimdension80746 ай бұрын
I totally agree with smoguli - continuous draw on a 15 or 20 amp breaker is limited to 80% of the breakers rating - ie, 20 amp breaker is limited to 16 amps continuous draw - ditto for a 15 amp breaker = 12 amps continuous draw - I believe Stage one chargers draw less than each because of safety reasons - like u have other items on the same circuit- best to go with a dedicated circuit ( no other items plugged in on the same circuit)
@YeOldeTraveller4 ай бұрын
I cannot speak for Canada, but the marked value of a standard circuit breaker in the IS represents a 3 hour limit. I would expect a continuous load of 15 amps to trip a 15 A breaker after about 3 hours. I have done this with backup systems where the charger was able to draw enough power for a long enough period to cause the outlet breaker of the generator to trip. I would be careful of pulling full rated power by design. That 80% derate is to keep things for warming up over time.
@benwouda11 ай бұрын
europe also has 380v and 3 phase allowing for 11kWH AC charging in selected cars
@soup142158 ай бұрын
Very helpful video.
@marclemieux82692 ай бұрын
When only 120-volt outlets are available, it is indeed possible to charge your EV significantly faster using a portable Quick 220 system that can provide you with either 2.7 or 3.8 kilowatts per hour depending on the availability of NEMA 5-15 or 5-20 Outlets. The Quick 220 system is a quality, fully ETL certified charging tool that enables an EV driver to obtain faster charging in areas with little charging infrastructure. However, you must follow the included instructions to the letter for safety purposes since you're dealing with 240 volts. As such, you must sufficiently educate yourself on the basics of electricity so as to ensure your safety and the source you're plugging into! When in doubt, consult an electrician! I have successfully used my Quick 220 system at my cottage, which has an old electrical panel that cannot accommodate an additional 240-volt breaker. Using my affordable Quick 220 system, I can obtain up to 12-15 miles per hour of added range to my EV.
@wrenchrad4 ай бұрын
Appreciate this well made clear vid and all the comments too, I’ve been shopping for a L1 EVSE for emergencies for my Kia EV6. I just want the J1772 plug with a fuse dongle, I have plenty of outdoor rated 12ga 15A-capable extension cords, anyone sell the connector without the cord?
@Truth1000.4 ай бұрын
should we worry about rain, snow or moisture? I see that you just went straight for it without hesitation, is it pretty safe? thanks
@MrSizewise3 ай бұрын
How much $ does it cause to charge on Level 1 at home?
@bassistdc3 ай бұрын
Actually, that's a charging cable, not a charger. The charger is built into the car. You probably know this. You are just referring to this wrong. No disrespect intended.
@gregyohngy5 ай бұрын
Always bring an extension cord with you! Your car might be farther than 10 meters away from the electrical outlet. I helped out a Hyundai EV with only his J-1772 charger. He sat for 5 hours before I arrived. Grab a Tesla to J-1772 adapter. You can use a Tesla charger, while at a brewery. 🍺
@rickywhisenhunt45827 ай бұрын
Recommended to only charge to 80% of battery capacity. Perhaps for long trips 100% is okay from time to time.
FYI at 12:20 - circuit breakers have built in 20% buffer, so a 15A breaker actually trips when a bit more than 12A is drawn.
@kevinmanan1304Ай бұрын
No it will trip a little above 15A. Your device can only do at most 80% due to RMS (root mean squared). AC current doesn’t move in a straight line so you’ll only get an average since it moves like a Sine Wave. If it were DC that would be a different current graph. Anyways always hire an electrician if you install these things. Don’t risk burning your house down because you didn’t know there was no buffer.
@justDudpool5 ай бұрын
You MUST understand that continuous use MUST be 80% of the rated circuit. For example- drawing 15 amps continuously on a 15 amp circuit is DANGEROUS! It will start a fire.
@RobertBrown-jz4qj6 ай бұрын
The nema 5-20 IS NOT USED IN BATHS OR KITCHENS. It might look similar but it is NOT nema 5-20. It is a GFCI. It should be 20 anps in the kichen only. All others will be 15 anps
@jschlock4485 ай бұрын
Level one does use more energy than Level two; my observation.
@hg60justice10 ай бұрын
evse are so cheap, wonder why they don't provide them with each car. my bolt euv came with an interchangable plug of both 120 and a nema 14-50 delivering up to 9kw. allow you to charge level 1 or 2. level 1 would work fine for us on most occasions, but having level 2 is better. i live nw of edmonton. it's within my return range in most conditions. whitecourt and spruce grove are our commuting destinations most times. your edmonton to calgary road trip grabbed my attention since it's close. now i know where i can road trip too.
@karlInSanDiego11 ай бұрын
The Ioniq Guy experimented with his Ioniq 5 (E-GMP) and revealed 31.5% charging losses by charging at Level 1 rates, which is criminally bad for a long-term charging solution. The manufacturers understand these large battery cars are so pitifully slow at Level 1 that they consider it to be an emergency mode only vs. a rational way to charge, but I know a lot of retirees, who drive infrequently and therefore assume this Level 1 route is cheap and easy and it still meets their minimal driving needs. If they knew it wasted 23% more of their electricity than using Level 2 and thus ultimately reduces the efficiency of their car's energy usage by ~1/4, I think they'd reconsider that choice. kzbin.info/www/bejne/d5qmhKGtpKamZsUsi=IhguTl59erD1F6Zn
@krerickson111 ай бұрын
My utility is about $0.10 per kwh and a 0-100% charge would be $6.00. 23% more is $7.38. It would take a whole lot of dollar-and-a-halfs to pay for a L2 charger.
@karlInSanDiego11 ай бұрын
@@krerickson1 the point is wasted electricity at scale. Not how much money you personally can save or not save. It's a Climate Crisis and a renewable energy challenge. Think beyond your personal wealth.
@scratchymaster11 ай бұрын
L1 also costs the inconvenience of not always waking up each morning to a full battery. L1 for most households still requires second gas car for days needing lots of driving. L2 install can be cheap if your breaker panel is close to your parking / charging spot. I only spent ~$60 on supplies at the hardware store. Plenty of L2 evse's available for under $150.@@krerickson1
@BrianOlmsted11 ай бұрын
You are loosing so much efficiency of the power using L1 power vs installing an L2 home charger using a 40-48amp connection @ 240V = 9.6-11.5kW. Get rid of that L1 connection ASAP as it should only really be used for emergency trickle charging on the road
@lukastembergerАй бұрын
What do you mean by "lose efficiency"?
@bighou23594 ай бұрын
I appreciate your video. Very informative. With being said, F*ck this EV sh*t. Too many drawbacks. Thanks again. Great video.
@spankytag7 ай бұрын
Thank you for being SO clear and concise. This was very helpful.
@malimoccoli548011 ай бұрын
DO NOT CHARGE AT 15A on a 15A circuit. There's are reason why stock chargers at set at 12A. Circuits are supposed to be used at 80%. If you used a 15A circuit at 100% for an extended period of time it will melt the wires in your house without tripping the breaker. Also advise agains using that silicone spacer. Outlets fail and burn when they are loose or not inserted properly due to higher contact resistance.
@rcpmac4 ай бұрын
Nonsense
@wyjpremium3 ай бұрын
This is true in North America (the NEC specifies an 80% limit for any continuous load on a circuit - higher spikes are permitted but anything that draws current continuously like a space heater or EV charger must be limited to 80%, so 12A on a typical 15A circuit). This is not necessarily true in other countries. Here in Australia there is no 80% rule and you can continuously draw the full rated capacity of a circuit (and manufacturer-provided EVSEs will default to using 100% of the circuit’s capacity, unlike in America).