Now that you've narrowed down the problem, the repair videos for each furnace part are all listed in this playlist: kzbin.info/aero/PLCo9SMjkdWBzorzNrARLKALj9fW7HzHMh
@AmreSupply
@AmreSupply 4 жыл бұрын
@@mavericktorch1619 Thanks for watching. If your furnace gives you multiple codes, and none of the switches are faulty then it could be a problem with the wire connects or a problem with the control board itself. The control board is pretty simple to replace but is usually a non-refundable part. You can see how to replace it here: kzbin.info/www/bejne/aoS8aZ-IoZ17jJI
@thastudent1741
@thastudent1741 4 жыл бұрын
Great video had this issue vacuumed the vent out put and while doing so I started it up and it stayed on...thanks for a clear and concise video my friend you have a sub for life no doubt.
@AmreSupply
@AmreSupply 4 жыл бұрын
@@thastudent1741 Thank you for subscribing Erik! We're happy to hear that the video helped you out!
@jolenehayes3398
@jolenehayes3398 4 жыл бұрын
This furnace comes on and stays on a couple weeks then surprises us and goes off until it decides to come back on.
@jeffster1070
@jeffster1070 4 жыл бұрын
Great video. One thing about the inducer blower. We had an issue with the inducer coming on, then shutting back down. Eventually things kicked in later on and were normal. Then it happened again, so I called an HVAC specialist, but by the time her came, the furnace was running normally. So more background, this obviously is in the winter, and we were getting cold spells. I was also setting the furnace very low at night (13ºC). I then realized that any condensation that perhaps built up during the night, as the furnace was off for a good 10 hours, was obstructing the flow of air from the roof inlet. Once I set the low temperate to 19ºC, the issue never reoccured. The furnace does cycle on once or twice during the night, but by morning, it'll start up right away. Came here because I think I have an issue with the flame sensor (it always comes on and stays on, but after 1 or 2 tries) -- but unsure if it's the Nest doing this to conserve energy.
@catrinaweinum2659
@catrinaweinum2659 10 ай бұрын
Thank you from a single mom whose furnace wouldn’t stay on at 3am. Luckily I found this video immediately with a comment about “powdery snow” and I said I think this is my problem. Cleaned the flame sensor, problem solved in under 30 minutes. Forever grateful for your content!
@AmreSupply
@AmreSupply 10 ай бұрын
You're welcome, we're just happy that the video helped you get your furnace running again!
@L.U.G.O.
@L.U.G.O. 6 жыл бұрын
Imagine this: 2 a.m. and -20° outside w furnace turning on and off... 3 small kids, mom and I freezing. Watched like 10 other videos and nothing helped. Watched this one and voila! The vent was blocked w powdery snow. THANK YOU SO MUCH. And thanks for speaking slowly and clear, I was able to follow you without any problem.
@AmreSupply
@AmreSupply 5 жыл бұрын
Thank you for sharing your experience! In -20° weather, houses do lose heat very quickly, we're glad that this video helped you finally narrow down the problem!
@gomasmas5727
@gomasmas5727 5 жыл бұрын
Last night 11pm 12° 2 KIDS 1 BABY nagging WIFE
@ryanpennington817
@ryanpennington817 4 жыл бұрын
@@gomasmas5727 here now ..new crib gonna try n trouble shoot
@aerinmiller5289
@aerinmiller5289 Жыл бұрын
​@@gomasmas5727 Jesus dude, stop hating the person you married. It' sounds like a dire situation especially with small kids. I'd be stressed as hell.
@amfromearth360
@amfromearth360 11 ай бұрын
that's one of my biggest fears man. glad u took care of it
@johncleary4775
@johncleary4775 5 жыл бұрын
This is hands down the best gas-furnace breakdown I have seen. I have been fixing my furnace as a home-jobber for years, without being fully aware of the relationship between my problems and the phase of operation of my furnace. This blew my mind, and I fixed my furnace on this cold autumn night. Thanks a bunch, from Kansas City.
@AmreSupply
@AmreSupply 5 жыл бұрын
Thank you for your kind words! We've worked hard on some of these video to explain the whole system more than just mentioning isolated repairs. We're glad you found it helpful! If you're curious we've created and animated some in-depth videos on water heaters. Let us know what you think! kzbin.info/www/bejne/eHm4gXmCl8drhLs
@Blahblah-g2i
@Blahblah-g2i Жыл бұрын
Q¹¹¹ ⁰
@kamalnasari8632
@kamalnasari8632 4 жыл бұрын
Sorry I forgot to mention sears installed our furnace 7 years ago , anytime I tried to watch the installer , he & his partner stopped working . They were talking spanish & I could not understand them , but as soon as I left them alone they start to work . As a 45 years mechanic I,ve never mind people watching me , but anyhow I call same man on thursday , he told me he comes monday which is today . I am reading & watching U & the others , so when the man come , he does not tell me nonsense . I thank U for your respond . GOD SPEED ❤
@AmreSupply
@AmreSupply 4 жыл бұрын
Its always good to ask questions to who ever is doing the work. Hopefully the service call helps narrow down the problem.
@Everclearish
@Everclearish 2 жыл бұрын
My furnace was igniting then shutting off then on again continuous with no heat. The sensor had very little corrosion but I cleaned it and reinstalled and works fine again. I appreciate your time in making this video. Saved me $$$ Thanks.
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're just happy that the video helped you get it running again!
@ronaldellis7310
@ronaldellis7310 Ай бұрын
I have NEVER worked on a furnace, but of course during a particularly nasty cold snap in Denver, the heat would only release lukewarm air. I could see that the flame would only ignite for a few seconds at a time. I went to part II on this, followed all the safety suggestions, cleaned the flame sensor, and it works like a charm! Thank you for this! (And yes, I'm ordering a spare flame sensor...)
@AmreSupply
@AmreSupply Ай бұрын
That's great to hear! Glad it worked out for you.
@lapointx6
@lapointx6 5 жыл бұрын
Saved me a service call and some cash. Mine was the flame sensor issue. (Goodman furnace) Removed it, cleaned it, reinstalled it and now it’s working great! Thank you.
@AmreSupply
@AmreSupply 5 жыл бұрын
You're welcome Aaron. We're glad the video helped you narrow down the issue!
@RedroomStudios
@RedroomStudios 4 жыл бұрын
wow, that is crazy - exactly the same as me including the brand name of the furnace. mine is about 10.5 years old. thankfully it turned out to be a super easy fix!
@MrLaddiator
@MrLaddiator 2 жыл бұрын
I’ve had a problem with my furnace for a while now and I thought I had tried everything. Was about to hire out a professional to come and check it out but decided to try and clean the flame sensor. I think that was the problem. 2 minute fix that probably saved me $100+. Thank you SO MUCH!!!
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're just happy to help!
@mauramcgrath2660
@mauramcgrath2660 4 жыл бұрын
I watched a number of videos looking for help in order to make a DIY attempt at fixing my furnace... and it was after watching this one that I felt confident that I could pinpoint the issue and solve it. My guess was the flame sensor and happy to report that locating and cleaning my flame sensor solved the issue and I have heat again!! Thank you!
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome Maura! We're happy that the video helped you confidently narrow down the problem! Cheers!
@edjuan8213
@edjuan8213 11 ай бұрын
This should be the first line of attack when you have a "Short Cycling Furnace Problem". I almost gave up after cleaning the furnace and checking the Nest thermostat, fan limiter, limit switches, replacing the air filter and fan capacitor, etc... I was ready to call the HVAC professional when I decided to give Google another try, I entered "Why does my furnace keep turning on and off", and I found this section (3:13) in your instruction exciting, (holy sugar!) cleaning the burners and flame sensor monitors are the solutions to my problem after all. It took me a day and a half to figure it out, I lost half of my hair scratching my head, thank you very much for your help, this post really made my day...
@AmreSupply
@AmreSupply 11 ай бұрын
Thank you for sharing! We are just glad that people are finding these videos helpful and when it comes to the flame sensor, it is the root of many furnace issues for a good number of people. Cheers!
@garethcooley1318
@garethcooley1318 Жыл бұрын
This is incredibly helpful. I don't understand why more of this information isn't readily available for those of us that are capable of doing simple repairs like this.
@AmreSupply
@AmreSupply Жыл бұрын
Thanks for watching we're glad you found it helpful! It takes a bit of time and knowledge to produce videos like these, and we have put a lot of effort into making very detailed troubleshooting series. If you're curious, there's a series on refrigerators that we just released: kzbin.info/aero/PLCo9SMjkdWBxXf2GEiSiunxAlN3ENxXGq
@donnychaos
@donnychaos 5 жыл бұрын
Probably one of the best produced videos about this topic. Content was really helpful and concise. 10/10. Thank you.
@AmreSupply
@AmreSupply 5 жыл бұрын
Thank you Donovan for your kind words! We try to make all of our videos clear and concise and we're glad you found it helpful. We just released a series on Water Heaters that you might be interested in, including one that explains How Gas Water Heater Works: kzbin.info/www/bejne/eHm4gXmCl8drhLs Cheers!
@Mrdealornodeal618
@Mrdealornodeal618 2 жыл бұрын
Great breakdown. This may just be one of the best informative videos in this category.
@AmreSupply
@AmreSupply 2 жыл бұрын
Thank you Will, we're just happy to help! We try to make all of our videos as detailed as this. If you're curious we have a "how it works" playlist which many people find helpful: kzbin.info/aero/PLCo9SMjkdWBxWwrWCmzvRMSi2kLo9bGdp
@jagadeesh2k9
@jagadeesh2k9 3 жыл бұрын
I had a problem and my furnace kept switching off after few minutes of heating in repeated cycles and that was the last issue you walked through. I had to change the filter which is just a month old and it fixed the problem. Can't understand how a one month old filter can cause a trouble but the solution you provided was spot on. Your videos are phenomenal and well explained to the point. A big thank you!
@AmreSupply
@AmreSupply 3 жыл бұрын
Thanks for watching, we're glad that you found the video helpful. Was the MERV rating different on any of the filters? If a filter was a higher MERV rating and more restrictive than the others, then it can cause the heat exchanger to overheat.
@lonesometinman3147
@lonesometinman3147 3 жыл бұрын
My experience: buy the least restrictive filter They are cheap 1.50 - 3.00 $ each and replace often especially if you got pets who shed inside the house .plus more efficient at moving the cool air in summer
@Humanthing123
@Humanthing123 3 жыл бұрын
Your video was very helpful in troubleshooting. The clear troubleshooting for each phase of operation made it easy to find the flame sensor was at fault. Thankfully managed to fix it on a dangerously cold night of -27°C (-17°F) My furnace would occasionally run normally. But every few hours, it would attempt to light 3 times, and shut off. I could hear the burners ignite for about 3 seconds, then they would shut off. Investigated the flame sensor. It was clean, but was loose and not close enough to the flame. Tightened the screw and re-adjusted so was in the flame path, and now it's working perfectly. Although you didn't mention that particular issue in the video, it still helped me narrow it down.
@AmreSupply
@AmreSupply 3 жыл бұрын
Thanks for watching. We're glad that the video helped you get your furnace working again after such a cold night. You are right that this video didn't go into all the details on the flame sensor. The flame sensor is actually just a rod that sits in the flame. It doesn't sense heat, it completes a circuit from the control board, through the flame sensor, through the flame to the burner or heat exhanger, and returns through the ground wire. The position of the flame sensor, a dirty flame sensor or a carbon buildup on the burner can all prevent this low voltage DC circuit from being completed. Hope this helps provide a little more context!
@diaperdan3
@diaperdan3 4 жыл бұрын
Great Video.. 4 am.. Zero degrees outside. House temp 55 degrees.. Furnace short cycling. Watched this Video.. Cleaned flame sensor.. Took care of problem.. One of the best video's for trouble shooting .. Thank You !!!! Happy Wife ,,Happy LIfe !!
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you for sharing, we're glad you found the video helpful! Sometimes it is just a simple fix!
@jenchamberlain7241
@jenchamberlain7241 4 жыл бұрын
Thanks Vance! Our furnace turned off on Christmas and you have saved us a lot of money and a cold Christmas day. Vance you're the man. XD
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome Jen! We're so glad that the video helped you keep your home heated on Christmas day!
@ikeavaughan
@ikeavaughan 3 жыл бұрын
I dont know whats more satisfying... the helpful tips or his perfect goatee
@AmreSupply
@AmreSupply 3 жыл бұрын
Thanks for watching. Why choose when you can have both in this video!
@ikeavaughan
@ikeavaughan 3 жыл бұрын
@@AmreSupply hehe thanks again for the help God bless
@Jet13lack
@Jet13lack 2 жыл бұрын
Thank you! It took 5 minutes to clean the flame censors and now my furnace is working properly again.
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome Anthony, we're just glad to help!
@sitindogmas
@sitindogmas 11 ай бұрын
you just help me keep my kids warm in the middle of January in W.V. 20 degrees outside with 8 inches of snow 😊 Thank You !!!
@AmreSupply
@AmreSupply 11 ай бұрын
Thank you for sharing we're just happy to help out especially on these cold winter days!
@mattfoy1376
@mattfoy1376 Жыл бұрын
Thank you for the excellent break down. Best video I've seen so far on this
@AmreSupply
@AmreSupply Жыл бұрын
You're welcome! We're just happy to share some good info!
@shaneconaway1079
@shaneconaway1079 2 жыл бұрын
Great video. It just confirmed my last fix is the right one. I had already been through cleaning the flame sensor, took the burners out and cleaned them, and thoroughly cleaned everything inside that I could, replaced the limit switches and the furnace would still decide to not ignite on occasion. I took the pressure switch tubing off and some water in there. After draining that and blowing it out good it has fired up without a hitch.
@AmreSupply
@AmreSupply 2 жыл бұрын
Thank you for watching, we're glad that the video helped you confirm and narrow down the problem.
@RedroomStudios
@RedroomStudios 4 жыл бұрын
at first I was sure the problem was going to be the igniter but after watching that video and allowing the furnace to try starting with the front panel off I could see that the igniter was working fine and I had flame for several seconds before it would shut off. I tried checking the flame sensor and wasnt too hopeful because it barely looked dirty. a quick clean with some fine sand paper, put it back in, turned the system on and it's running perfect! I also think the electrical connection may have been loose so made sure that was tight. thank you so much for this great helpful video! saved me at least $150 for a service call and who knows if they would have tried to sell me something I didnt actually need. I hope this business model is working for AMRE. I was totally ready to order parts from you guys if I needed them.
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you for sharing your experience, we're glad the video helped you out! You are right a loose connection, corrosion on a terminal, or a frayed or broken wire can cause the same issues as a dirty flame sensor. Overall AMRE has come a long way in 50 years we're fortunate to be able to help people out with these videos! Thank you for the support and we'll still be around next time one of your appliances or fixtures needs a new part! Cheers
@RedroomStudios
@RedroomStudios 4 жыл бұрын
@@AmreSupply right on! you guys are the best!
@kevinb120
@kevinb120 Жыл бұрын
Excellent video! I found that after remodeling work, even with the system off, all of my sensors got dirty. This video narrowed it down to the main culprit, but gave me the confidence to explore my system further and check/clean every sensor carefully. Just took a tiny bit of dust to throw some of them off.
@AmreSupply
@AmreSupply Жыл бұрын
Thank you, we're just glad that the video helped you out! The flame sensor is particularly sensitive to a buildup of dust or carbon as it relies on a small DC current to travel from the control board, through ions in the flame through ground. This is how it proves that a flame is present. The flame sensor is nothing but a small metal rod. Nothing special about it.
@jlo7314
@jlo7314 6 жыл бұрын
I'm a first time home owner. This helps a lot thank you
@AmreSupply
@AmreSupply 6 жыл бұрын
Thanks J Lo, we're glad you found this video helpful!
@renatodecastro1306
@renatodecastro1306 Жыл бұрын
Thank you, with your help I was able to fix my furnace in the coldest day. I really appreciate it.
@AmreSupply
@AmreSupply Жыл бұрын
You're welcome, we're just glad to help!
@TheMan4407
@TheMan4407 4 жыл бұрын
Thank you for your helpful video. Had a dirty flame sensor. Removed and polished, and now everything is back to normal. Thank you!!
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome! We're glad that the video helped you out!
@Johnslist
@Johnslist 4 жыл бұрын
Well done and very educational. I hesitantly called a guy out who started immediately with the 'I hope it's not the heat exchanger,' for which I'd throw him out. He was pretty good at testing everything methodically, as an engineer though I was questioning things - enough for me to realize he didn't get it and just wanted to throw parts at it. These things are not rocket science so I'm sick of these technicians who come out with more stories than Shakespeare. I learned more from you in 5 minutes. I already suspected he flame sensor, but will review limit switch as well. The 'tech' wanted to replace the circuit board for $1800! I found them online for under $100 (btw, that is what I used to do so I don't need his warning of electrocution or 'every year the fire departments find people in attics' (he said that!). The other annoying thing is finding info in materials or on company's website - everything just refers you to other criminals, I mean 'techs.'
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you for sharing your experience and we're glad that you found the video helpful. This was one of our goals with the furnace series is to help homeowners gain a bit of knowledge. People go through the same stress with vehicle repairs, a little bit of knowledge can help prevent a mechanic from doing unnecessary work or over charging for a simple repair. Also $1800 is highway robbery for a control board. With the power disconnected these boards are very simple to replace.
@Johnslist
@Johnslist 4 жыл бұрын
@@AmreSupply Yep, you will do far better being transparent and honest than these hacks out there trying to get rich off every single call. Good branding! I've not swapped the board because I've been doubtful and prefer to review the other items like you showed. Business is so easy, but there are still these old school clowns hanging on to ideas that 'people don't know' (tell 'em it's danegerous.'), they'll be gone soon enough, I hope.
@shw4083
@shw4083 Жыл бұрын
I called a guy which costed $180 came over, and only cleaned my furnace, then suggested me to replace the furnace, but didn't solve my issue. I cleaned they flaming rod myself and now it worked for about 3 months. but now, the furnace works only when the cover is opened, as soon as I put the cover on, it stops, even with the filter took off. Could you help suggest what's the issue? thanks
@Johnslist
@Johnslist Жыл бұрын
@@shw4083 They suck, as do plumbers, AC techs, water heater and appliance people, someone is teaching them bad habits - how about honest work for honest pay? Crooks.
@Del_Keba
@Del_Keba 11 ай бұрын
@@shw4083did you ever figure this out? My error code is reading limit switch, if I have both doors on it will run for 5 minutes then shut off then cycle again a few more times before lockout. If I leave the flame door off it will just keep running without shutting off.
@Schroonman
@Schroonman 2 жыл бұрын
By far one of the best DIY videos. I'm very handy and have been fixing my own appliances etc for years, including putting a new circuit board on my furnace a few years back. Is was having short cycle issues for the past 2 years and have done EVERYTHING mentioned in your video except for ONE thing! No other video or website that I've come across has talked about or mentioned the LIMIT SWITCH!! Thank you and wish me luck!!
@AmreSupply
@AmreSupply 2 жыл бұрын
Thank you, we're glad that you found the video helpful! We really try to make all of our tutorials informative especially with graphics and concise information. Best of luck with the repair!
@Schroonman
@Schroonman 2 жыл бұрын
UPDATE!! I first want to say that this is the ONLY DIY video that mentioned the LIMIT SWITCH as a possibility. Well I'm here to update everyone and can now report that the LIMIT SWITCH was EXACTLY my problem. I had the Short Cycle problem for a couple of years and had done EVERYTHING to correct it myself. Well I finally heard this info and purchased a NEW limit switch online for $24..PROBLEM SOLVED!! I want to thank AMRE Supply for these videos and will now subscribe to their channel! Thank You AMRE, you guys are lifesavers!!
@mbhooshan
@mbhooshan Жыл бұрын
Thanks for explanation. Looks like I fixed my furnace issue today.
@AmreSupply
@AmreSupply Жыл бұрын
You're welcome, we're just glad to help!
@hyperfilmprod
@hyperfilmprod 2 жыл бұрын
Thank you very much! It would have been a very cold night here without this video!!! Very much appreciated.
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're just happy that the video helped you out! Was it the flame sensor?
@hyperfilmprod
@hyperfilmprod 2 жыл бұрын
@@AmreSupply Yes it was. At 5pm on a Saturday of a long weekend in February, it wasn't a happy discovery. But your excellent video had us up and running in no time. Thanks again (and subscribed)!
@AmreSupply
@AmreSupply 2 жыл бұрын
@@hyperfilmprod We're glad to hear it, and thanks for the subscription!
@LewisShieldsUS
@LewisShieldsUS 4 жыл бұрын
Vance, you're a good teacher; a calming influence and a motivational spark. With your help, I'll fix this! Thank you.
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you Carol for your kind words! It means a lot to know that our videos are helping to inspire people! We really have made an effort to try to help people gain more knowledge so that they can do the repair themselves or just have a better understanding for when they communicate with a professional. All the best to you!
@Goodmusiq9
@Goodmusiq9 3 жыл бұрын
Wow thanks to your video, I was able to diagnose my furnace and resolve the problem!!! Gratitude!
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome, we're just happy to have helped out!
@paranoma87
@paranoma87 2 жыл бұрын
Awesome! Just fixed my furnace with the help of this video!
@AmreSupply
@AmreSupply 2 жыл бұрын
Thank you for watching, we're glad to hear that!
@nicolem376
@nicolem376 2 жыл бұрын
THANK YOU! It’s 16 degrees on a Friday night here and my heater pilot would not stay on. It didn’t match your video exactly because the pilot would continuously light and go off within a couple seconds but the fan was blowing the entire time. Regardless, I cleaned the flame sensor (which barely looked tarnished) and it immediately fixed the problem. I cannot thank you enough!!!!! ❤️❤️❤️❤️❤️❤️❤️❤️❤️❤️❤️❤️❤️❤️❤️
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're just happy to help! It could be an issue with the thermocouple, so it might re-appear. kzbin.info/www/bejne/aXauk4afdq-sn6s Also if you have a multimeter you can test the thermocouple voltage to see if it is producing enough voltage to keep the pilot flame lit. If you have a spark ignition then your furnace might work slightly different than the thermocouple example as before. You can test the voltage similar to the steps in this video: kzbin.info/www/bejne/g6mZo413br6rrJY
@regina6827
@regina6827 2 жыл бұрын
I ❤❤❤ videos offering very DETAILED graphics!!!🙌👌😃
@AmreSupply
@AmreSupply 2 жыл бұрын
Thank you! I think you'll love these videos as well, we have a whole playlist showing "how it works" all with detailed graphics: kzbin.info/aero/PLCo9SMjkdWBxWwrWCmzvRMSi2kLo9bGdp
@luiscecilio8807
@luiscecilio8807 2 жыл бұрын
thank man, You are a teacher and a money saver. I ma very grateful for your teahings and savings. Soon i will make an offer for charity in your honor. Bets regards
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, and we appreciate the warm thoughts! Cheers!
@michaellangell4667
@michaellangell4667 2 жыл бұрын
Never worked on a furnace and had it up and running in an hour. Thank You!!!
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're just happy to help!
@xdmartx
@xdmartx Жыл бұрын
Helped me troubleshoot my furnace. Thanks!
@AmreSupply
@AmreSupply Жыл бұрын
You're welcome, we're just happy to help!
@LukeWarmwater-yb5lx
@LukeWarmwater-yb5lx 2 ай бұрын
Excellent playlist, Thank You.
@AmreSupply
@AmreSupply 2 ай бұрын
You're welcome, we're just happy to help!
@casandrawheeler917
@casandrawheeler917 Жыл бұрын
Thank you for the video!!! Our sensor needed to be cleaned, and now we have no issues! :)
@AmreSupply
@AmreSupply Жыл бұрын
You're welcome, we're glad that the video helped you get your furnace working again!
@SunilNethisinghe
@SunilNethisinghe 3 жыл бұрын
Very calm and clear, well explained in a logical sequence. Thank you.
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome, we're glad that you found the video helpful!
@I.rod.2022
@I.rod.2022 2 жыл бұрын
This video is such a life saver. I just needed to clean the flame sensor! A guy wanted $200 dlls to do that. 🤣.
@AmreSupply
@AmreSupply 2 жыл бұрын
We're glad to hear that the video helped you with that easy fix!
@frankmcwain139
@frankmcwain139 4 жыл бұрын
This was the first and only video I looked at and the answer was easy and clear! Thank you! Sincerely, from a do it yourselfer! Frank
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome Frank, we're glad that the video helped you out! All the best to you!
@transam4555
@transam4555 3 жыл бұрын
One of the best informative videos I've ever seen on KZbin great job guys.. thanks to this video I have fixed my issue. Bad limit switch
@AmreSupply
@AmreSupply 3 жыл бұрын
Thank you so much! We put a lot of effort into the scripts, graphics and the narration to make these videos as good as possible. We're glad that the video helped you narrow down the problem!
@pt4822
@pt4822 3 жыл бұрын
Thanks AMRE and this video. My furnace keeps turning on, ignitor would ignite gas then off for three cycles. It's a Lennox G40UH. The diagnostic lights indicate bad ignitor. So replaced ignitor. Still the same. Then cracked open a beer and watched this video. Symptoms point to bad flame sensor in second part of video. So I cleaned the flame sensor as instructed. Lo and behold, it worked.
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome! A dirty flame sensor can create a lot of problems. We're glad the video helped you fix the problem!
@stevenshane4943
@stevenshane4943 4 жыл бұрын
Thank you! It was the flame sensor being dirty. The flame would shut off after 7 seconds. Now working great.
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome Shane! We're glad that this video helped you narrow down the problem!
@maurkowalchuk
@maurkowalchuk 2 ай бұрын
Excellent Video > Watched the options , tried cleaning the flame sensor !0 min job for me and now it is not cycling on and off all the time ! thanks for the help and probably saved me $200
@AmreSupply
@AmreSupply 2 ай бұрын
Thank you, we're glad that the video helped you out!
@riannebarnes7200
@riannebarnes7200 2 жыл бұрын
Thank you! Thank you! Thank you!!! -5° my furnace stopped in my new-to-me home. This helped me remedy the situation myself.
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're glad that the video helped you get your furnace working again!
@kurtisca
@kurtisca 3 жыл бұрын
Awesome video, great info, excellent graphics and clear communication - Top notch work!
@AmreSupply
@AmreSupply 3 жыл бұрын
Thank you, we're glad that you found it helpful! If you're interested we just released a series on oven and stove troubleshooting, including some "How it Works" videos. They are the same level of quality as this video: kzbin.info/aero/PLCo9SMjkdWBzSdZB9Un3GKKI0Iohlpf9a
@detaux
@detaux 3 жыл бұрын
Had the exact issue you described with the shuts off after ignition. Per your directions I cleaned up the flame sensor and it turned on immediately. Thanks!
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome! We're glad that its working again!
@Luxandruz
@Luxandruz 2 жыл бұрын
If I were killed in war, I’d trust this man to step in and be my wife’s new husband.
@AmreSupply
@AmreSupply 2 жыл бұрын
AMRE has you covered
@shwndh
@shwndh Жыл бұрын
Damn! That’s a lot of confidence
@rjkulman8990
@rjkulman8990 5 жыл бұрын
tks very much, it was a dirty flame sensor, cleaned and is now working, will buy another as a backup - great video
@AmreSupply
@AmreSupply 5 жыл бұрын
You're welcome Rj, thanks for watching! While you're at it its a good idea to have an extra furnace ignitor on hand as a backup. Ignitors are a common point of failure as well.
@pmschaaf
@pmschaaf Жыл бұрын
This video just saved me a bunch of bucks and time. Simple cleaning of my flame sensor probe fixed it!!! so happy and appreciative. 😊
@AmreSupply
@AmreSupply Жыл бұрын
Thanks for watching, we're glad that the video helped you out!
@Jamesdddddd
@Jamesdddddd 8 күн бұрын
Thank you!!!! Cleaning the flame sensor did the trick.
@AmreSupply
@AmreSupply 6 күн бұрын
You're welcome, we're glad to hear it's working again!
@kennethterry6453
@kennethterry6453 5 жыл бұрын
Thanks for the great information. I found it very helpful with troubleshooting my furnace. Your honesty and candor is greatly appreciated.
@AmreSupply
@AmreSupply 5 жыл бұрын
You're welcome Kenneth and thank you for your kind words! We're glad this video helped you out!
@robertbeam8669
@robertbeam8669 2 жыл бұрын
Great video. It was my limit switch...just needed cleaned with emory cloth. Furnace fired right up and kept going. Thank you for your time.
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're glad that the video helped you out!
@juarez33emilio
@juarez33emilio 3 жыл бұрын
Your video easily saved me hundreds.
@AmreSupply
@AmreSupply 3 жыл бұрын
Thanks for watching, we're glad that it helped you out!
@KingHarry1
@KingHarry1 2 жыл бұрын
You mentioned in the beginning of this video the different kinds of safety switches - pressure switch, flame sensor, flame rollout switch, and the limit switch and what they do. I was wondering what the flame rollout switch does and the signs of when to replace it? Your videos are awesome and I love this channel. Thanks for all the education!
@AmreSupply
@AmreSupply 2 жыл бұрын
Thank you, we're quite glad that you're finding the videos helpful! The flame rollout switch monitors the burners, if there is an airflow issue and the flames are "rolling" out the front of the burner, then the switch will disconnect power. If you notice a lot of carbon buildup around the front or and the switch then that indicates a flame rollout issue, and that will need to be investigated further. If there are no signs of a flame rollout, but the switch is having issues, then it could be a faulty switch. The flame rollout switch should have continuity at room temperature. If it doesn't then it's faulty and should be replaced. This kind of failure is not that common though.
@anthonyfalbo5203
@anthonyfalbo5203 4 жыл бұрын
Hi AMRE! wanted to thank you for this great video. i've never worked on my furnace before (outside of filter changes) and within minutes i had my issue identified (faulty temp sensor). you saved me when i was in a pinch!
@AmreSupply
@AmreSupply 4 жыл бұрын
Hi Anthony, thank you for sharing your experience! We are happy to hear that this video helped you out in a difficult time!
@dereksosa5801
@dereksosa5801 2 жыл бұрын
This is the best video I've found thanks for the tips
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome we're just happy to help!
@georgegarcia5763
@georgegarcia5763 4 жыл бұрын
Great video saved me a ton of money! One cold night spent due to a dirty flame sensor! Thanks for a quality video!
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome George! We're glad you were able to get your furnace running again!
@AjAj-ef4yv
@AjAj-ef4yv 4 жыл бұрын
Wow. Great great video! (both audio, graphics and explanation) Thank You (you can have a continuous series :))
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you Aj, we're glad that you liked the video! The furnace series was a fun one to make and currently we're working on a series for Oven and Stove repairs. All the best to you!
@AmreSupply
@AmreSupply 3 жыл бұрын
As mentioned here is the Oven and Stove series which includes some "How it Works" videos. They are quite detailed with some 3D and 2D graphics: kzbin.info/aero/PLCo9SMjkdWBzSdZB9Un3GKKI0Iohlpf9a
@markrafferty3573
@markrafferty3573 4 жыл бұрын
Thanks for making this video. It saved me a service call on Christmas Day. A little sand paper and the flame sensor was working perfect again.
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome Mark, we're glad that the video helped you out on a day where a service call would have been more difficult or expensive! All the best to you!
@frontsidebagco7055
@frontsidebagco7055 3 жыл бұрын
Thanks for helping diagnose our furnce. great videos!
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome, we're just glad that you're finding the videos helpful!
@JoePAcalaughs
@JoePAcalaughs 7 ай бұрын
Woohooo thanks! Was water in the pressure switch tubing! You rock 🪨 💪🏻
@AmreSupply
@AmreSupply 7 ай бұрын
You're welcome, we're glad the video helped you narrow it down!
@jboston984
@jboston984 2 жыл бұрын
This is a great video very detailed but I’d like to add something to this. If the heater keeps shutting down and you have done all this! Check your condensate pump line. It might be frozen if it is up in the attic and it’s like 6 degrees outside. So if your condensation pump is hooked to your heater it will shut it down as well.
@AmreSupply
@AmreSupply 2 жыл бұрын
Thank you for watching. Yes that is an excellent tip!
@marilyn6068
@marilyn6068 4 жыл бұрын
Wish I had seen this video before it cost me $60. It was the flame sensor. Will know to watch your video next time. Great video.
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you Marilyn, we're glad that you found it informative! If needed you can save this playlist for later as it has all the furnace repairs and troubleshooting. kzbin.info/aero/PLCo9SMjkdWBzorzNrARLKALj9fW7HzHMh As well, we also have videos on water heater repairs, which is a good reference kzbin.info/www/bejne/eHm4gXmCl8drhLs
@jamestingay11
@jamestingay11 4 жыл бұрын
Great video that saved me a service call. The flame sensor just needed a cleaning
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you for watching James. Sometimes its just a simple fix! We're glad that the video helped you out!
@scottthief60
@scottthief60 3 жыл бұрын
Thanks y'all! I cleaned my flame sensor and it's working great now. You guys rock!!
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome Scott, we're just happy to have helped!
@IanInbody
@IanInbody 3 жыл бұрын
Wondeful video, now have heat again after a quick free fix!
@AmreSupply
@AmreSupply 3 жыл бұрын
Thanks Ian, we're just happy to help! If it was a quick fix, was it the flame sensor?
@sabastianortiz2469
@sabastianortiz2469 3 жыл бұрын
thank you so much!! just cleaned the flame censor and works like a charm🙏
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome Sabastian, we're glad that cleaning the flame sensor worked!
@italianstallion69420
@italianstallion69420 4 жыл бұрын
My furnace works just fine I just like watching these videos
@AmreSupply
@AmreSupply 4 жыл бұрын
Thanks for watching! We're glad that you're enjoying the videos!
@dancingoyster
@dancingoyster 4 жыл бұрын
Great video. Short, concise and accurate. Thank you for your help. Got me out of a bind late on a Sat night.
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome! We're glad that the video helped you out! What in the end fixed your problem?
@gomasmas5727
@gomasmas5727 5 жыл бұрын
Thx u. God bless I Survived 14 degree weather cleaned everything put it back Thx so much god bless u again
@AmreSupply
@AmreSupply 5 жыл бұрын
Thank you Tom for sharing your experience. We're glad you were able to get everything back up and running!
@gomasmas5727
@gomasmas5727 5 жыл бұрын
Hi I have question my igniter turn on three times then my fire starts and my light is blinking 3 short and 4 long ones once the fire starts then stay lit everything else is normal the only problem is my igniter light up 3 * then I'll leave my gas releases them the fire and I change all three senses what do you think the problem is
@AmreSupply
@AmreSupply 5 жыл бұрын
Best to check what that code is. The code is different for each model so check your furnace manual or the diagram which might be on the back of the furnace door. Also if the furnace ignites but doesn't stay lit or takes several times to stay lit, then it might be worth cleaning or replacing the flame sensor. That would be the first place to start.
@gomasmas5727
@gomasmas5727 5 жыл бұрын
Im getting three short and for long(34) bryant. Model # 310aav036070adja. Ignitor Light Up 3 times and shut off with the machine on then only gas and fires up
@AmreSupply
@AmreSupply 5 жыл бұрын
@@gomasmas5727 The 34 code for that model is a "Ignition Proving Failure" what you are seeing is the furnace try to light 3 times then shut down and lockout until trying again. The furnace igniter could be faulty or starting to fail, you can learn how to replace it here kzbin.info/www/bejne/gnKkioCFpbuZY5o Also the burners could be dirty and obstructed, it best to clean them as part of regular maintenance kzbin.info/www/bejne/Z5jMgX-ohMeMmJY
@juanzayas3844
@juanzayas3844 2 жыл бұрын
Absolutely loved the video. I will definitely save and pass it along.
@AmreSupply
@AmreSupply 2 жыл бұрын
Thank you!!
@domingosramos6811
@domingosramos6811 2 жыл бұрын
thanks for information, Vance you just save me at least one hundred, i did remove de flame detector clean it, and put it back ...worked, thanks from new jersey
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're just glad to help save you some money!
@ricklee490
@ricklee490 11 ай бұрын
Thank you man you just saved me $150.
@AmreSupply
@AmreSupply 11 ай бұрын
You're welcome, we're just happy to help!
@jaypryor6875
@jaypryor6875 4 жыл бұрын
Nice vidio. You did a great job and saved me a repair bill ! Thanks jay
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome Jay, we're glad that the video helped you!
@bdcher01
@bdcher01 3 жыл бұрын
Another potential issue that could cause furnace turning itself off after running (with gas on) for a short time is that the outdoor exhaust and intake ports/pipes were installed incorrectly. If both pipes have openings (outside) next to each other, such as both facing down, then the intake may be sucking in the exhaust gas, causing a lack of fresh air/oxygen for combustion. Fixed easily by making one pipe face out and other facing down. Though illustrated clearly in instruction manuals, some installers don't do this right.
@AmreSupply
@AmreSupply 3 жыл бұрын
Hi Boris, thank you for watching. That is a great point and another good thing to look for when troubleshooting this!
@dalecannon6769
@dalecannon6769 2 жыл бұрын
Should the exhaust face down(with a elbow?) Or just no fittings at all- what about fresh air intake-a 45 elbow-or straight pipe also
@eduardoestrada8648
@eduardoestrada8648 2 жыл бұрын
Thank you so much!!! The temperature dropped to 30 degrees today and the furnace kept on shutting off after ignition! I just needed to clean the sensors!!!!!
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome Eduardo, we're glad that the video helped you get your furnace working again!
@hulkgarage454
@hulkgarage454 11 ай бұрын
Thank you for helping me fix my furnace.
@AmreSupply
@AmreSupply 11 ай бұрын
You're welcome! What in the end fixed your problem?
@hulkgarage454
@hulkgarage454 11 ай бұрын
@@AmreSupply cleaning the flame sensors I have 2 on my unit.
@joefarwana3171
@joefarwana3171 5 жыл бұрын
Thank You. I found dirty flame sensor just like you explained. Cleaned it and the family never new the heat was down in a very cold night.
@AmreSupply
@AmreSupply 5 жыл бұрын
You're welcome Joe, we're happy to hear that this video helped you out. Sometimes its an easy fix! Cheers!
@benshively1455
@benshively1455 2 жыл бұрын
Thank you. I was able to fix the furnace on a cold Sunday day.
@AmreSupply
@AmreSupply 2 жыл бұрын
You're welcome, we're just happy to have helped!
@davidbradley3074
@davidbradley3074 4 жыл бұрын
You have a great set of error debugging videos, well done and thanks!
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you David, we're glad you're finding the videos helpful! We definitely try to help people understand the system behind these problems not just the isolated problem itself. We're actually working on quite an in-depth series troubleshooting oven and stoves which will be a great one to share with the world. Cheers!
@AmreSupply
@AmreSupply 3 жыл бұрын
As mentioned here is the Oven and Stove series which includes some "How it Works" videos. They are quite detailed with soe 3D and 2D graphics: kzbin.info/aero/PLCo9SMjkdWBzSdZB9Un3GKKI0Iohlpf9a
@readcomics
@readcomics 9 ай бұрын
Thank you for your guidance, it was the ignitor for us
@AmreSupply
@AmreSupply 9 ай бұрын
You're welcome! We're glad the video helped you narrow it down!
@Christopher-fz4cw
@Christopher-fz4cw 4 жыл бұрын
Thank you so very much for making this video. You guys ROCK! The speaker was so very easy to understand, he enunciates everything perfectly! I FINALLY was able to fix our central heater, after weeks of going without. Tonight my family gets to stay warm for once. Thanks!
@AmreSupply
@AmreSupply 4 жыл бұрын
You are welcome Christopher! We're happy to heat that this video helped you out! What finally solved your problem in your furnace?
@Christopher-fz4cw
@Christopher-fz4cw 4 жыл бұрын
@@AmreSupply It was the flame sensor on my really old but really reliable Goodman furnace. I did exactly as stated in the video and took it out and cleaned it with some steel wool, and voila! Household heat!
@AmreSupply
@AmreSupply 4 жыл бұрын
@@Christopher-fz4cw Flame sensor issues are still common even with a reliable furnace. We're glad that it was a simple fix for you!
@JohnKaufmann
@JohnKaufmann 3 жыл бұрын
Nope sure there could be a better video on the topic. Nailed it right down to setting up bookmarks in the video for quick reference. BEST IN CLASS
@AmreSupply
@AmreSupply 3 жыл бұрын
Thank you, we're just happy to help!
@watertekmusic
@watertekmusic 16 күн бұрын
I'm getting a 4 blink error, which on my Intertherm/Nordyne propane furnace (Canada), says that there was an ignitor failure. I'm going to test continuity on the ignitor, and then...troubleshoot from there.
@AmreSupply
@AmreSupply 3 күн бұрын
Yes that sounds like a faulty ignitor, easy part to swap out to narrow down.
@Dansk55
@Dansk55 4 жыл бұрын
Wow I finally figured out my problem after fixing 3 relays in the motherboard (clicking noises). There was some dirt in the ignitor. Cleared it up and now the heat is on!! Thanks
@AmreSupply
@AmreSupply 4 жыл бұрын
Thanks for watching. Cleaning is always a good idea, its such a simple thing but it can definitely help. We're glad you have things up and running again.
@markdahl9453
@markdahl9453 3 жыл бұрын
Thank you very much for the video !!!! God bless you and America !!!! 😎😎🏁✌️
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome Mark, we're glad that you found it helpful!
@helmut926
@helmut926 4 жыл бұрын
You saved me a lot of money! I had a dirty flame sensor
@AmreSupply
@AmreSupply 4 жыл бұрын
You're welcome Jonathan! We're happy to hear that the video helped you out!
@tkienzle22
@tkienzle22 3 жыл бұрын
Thank you this video helped me get my furnace going it was my flame sensor I pulled it out clean it off on my jeans and stuck it back in and its working great.
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome Tim, we're happy to hear that the video helped you get it working again!
@creepybunny255
@creepybunny255 3 жыл бұрын
Most helpful video so far. Thanks.
@AmreSupply
@AmreSupply 3 жыл бұрын
You're welcome! We're glad that you found it helpful!
@MattAnonymous
@MattAnonymous 5 жыл бұрын
Thanks Tony Stark! (seriously though, this is a great video)
@AmreSupply
@AmreSupply 5 жыл бұрын
Thanks for watching! You're not the first one to make the Tony Stark comparison but we're glad you found the video helpful!
@SpaceRanger187
@SpaceRanger187 5 жыл бұрын
I did all that and my furnace shot off threw the ceiling and is now off fighting crime..Shouldn't have taken Matt's comment as a joke
@MoeKnowsBest..MGA..
@MoeKnowsBest..MGA.. 4 жыл бұрын
Omg you saved us tonight. It was our flame sensor being dirty and needing to just be cleaned and reinstalled. Once done it stayed lit and warmed up. Thank god because it was already 58 degrees and still dropping. We r changing the filter in the morning too just in case.
@AmreSupply
@AmreSupply 4 жыл бұрын
Hi Moe, thank you for watching! We're glad that the video helped you get your furnace running again!
@chueyang7221
@chueyang7221 4 жыл бұрын
Awesome video! According to the video my flame sensor needed a cleaning. Furnace is up and running fine now, hopefully this solves the problem
@AmreSupply
@AmreSupply 4 жыл бұрын
Thank you! We're glad you found the video helpful! As well dirty burners can interfere with the flame sensor, so you have problems again, make sure that the furnace is clean!
@chueyang7221
@chueyang7221 4 жыл бұрын
@@AmreSupply The flame sensor was cleaned yesterday morning, the furnace work fine all day but now it has the same problem today. The flames comes on for about 10 seconds and then shuts off and the cycle just keeps repeating. What else could be the problem?
@AmreSupply
@AmreSupply 4 жыл бұрын
@@chueyang7221 For the flame sensor to work it needs to be positioned in the flame and the burners need to be clean. There needs to be a path to ground from the burners to the furnace frame. If you have a multimeter you can test from the metal on the burner to the furnace frame to see if there is resistance or continuity. If there is no continuity then the flame sensor will not work as the circuit will not be completed. As well make sure that the flame sensor connections are secure and that there is no corrosion on the terminals to the control board.
@StuffDoing
@StuffDoing 5 жыл бұрын
This video just saved me a bunch of money! THANK YOU SO MUCH!!!
@AmreSupply
@AmreSupply 4 жыл бұрын
You are welcome Jake and Victoria! We're so glad the video helped you out!
@jaimegonzalez6926
@jaimegonzalez6926 5 жыл бұрын
Awesome explanation keep them videos coming
@AmreSupply
@AmreSupply 5 жыл бұрын
Thank you Jaime! We've got more videos in the works! Check out our youtube channel for more!
@AmreSupply
@AmreSupply 5 жыл бұрын
Just an update, we have a whole series on Water Heaters that you might find informative: kzbin.info/www/bejne/eHm4gXmCl8drhLs Cheers!
Furnace Not Blowing Hot Air - Explained | Repair and Replace
2:23
AMRE Supply
Рет қаралды 150 М.
Counter-Strike 2 - Новый кс. Cтарый я
13:10
Marmok
Рет қаралды 2,8 МЛН
УЛИЧНЫЕ МУЗЫКАНТЫ В СОЧИ 🤘🏻
0:33
РОК ЗАВОД
Рет қаралды 7 МЛН
I'VE MADE A CUTE FLYING LOLLIPOP FOR MY KID #SHORTS
0:48
A Plus School
Рет қаралды 20 МЛН
Troubleshooting Gas Furnace Cutting Off Randomly!
19:06
Jeff’s HVAC Adventures
Рет қаралды 10 М.
Furnace turns on then turns off after seconds - Common Causes
6:30
DIY with Michael Borders
Рет қаралды 165 М.
Furnace Troubleshooting - Common Problems | Repair and Replace
7:36
Furnace Won’t Turn On? Here Are 5 Easy Things To Check
12:02
The DIY HVAC Guy
Рет қаралды 77 М.
HVAC Furnace Short Cycling - How High Limit Switch Works
18:45
Word of Advice TV
Рет қаралды 105 М.
Gas Furnace Turning Off? Here's What Might Be Happening
15:56
Taddy Digest
Рет қаралды 243 М.
Furnace Keeps Shutting Off - Furnace Repair
2:49
FIX IT Home Improvement Channel
Рет қаралды 801 М.
Counter-Strike 2 - Новый кс. Cтарый я
13:10
Marmok
Рет қаралды 2,8 МЛН