That transformer in that 15kW inverter is about the same size as my 5kW unit, I noticed with all off the shelf inverters is the transformers are way undersized. Yes it will do the 15KW but with poor efficiency dropping below 93% 7% is a whopping 1050Watts of heat in that case, it will not last long. Also those little TO-220 mosfets irfb4110 all up 32 4 groups of 8 switching 300Amps at 50V, just a matter of time before it goes pop, or be sure to keep load at a few KW max no more, it will last then.
@IanTester3 жыл бұрын
Note that this is an old style of inverter and is not as efficient as newer designs. The newer ones first use a DC-DC converter to get up to the required voltage, and then switch that with mosfets. I can't remember what these two types of inverters are called and some googling mostly turns up solar power websites.
@bjtaudio3 жыл бұрын
Power Jack's definition of continuous power is full load for 10minutes or less, mine is full load + 10% for years. It really simple if anything gets hot and fans a running at full power then in not true continuous. My inverter only gets warm may be 15 degrees above room temperature, no fans needed.
@coreybabcock2023 Жыл бұрын
The thicker wire is to handle the amp draw without much voltage drop
@bobstockwell39115 жыл бұрын
the best Controller to use on this Inverter is the 100 amp Bluetooth Victron for $900
@joseperniarombos86793 жыл бұрын
Muy bueno tu canal, lastima que no lo das en español, la traducción de youtube no es la correcta. Pregunto lo siguiente, el equipo tiene entrada de alimentación en fase dividida ( 240/120 V) ?. Si es así cuenta con cargador de Baterías ?. Has realizado pruebas de cargas con un banco de resistencias, para determinar su potencia real que describe el fabricante ?. Saludos desde el estado de Barinas Venezuela. Soy ingeniero electrónico, técnico superior en Electrónica y técnico en Telecomunicaciones. Mi especialidad son los sistemas de Energía. Me gusta tu canal amigo.
@repairman18084 жыл бұрын
How this thing may be 15Kw if the power transformer is not more then 5Kw. A Triad Magnetic 5Kw transformer is 11 inches OD but this one is smaller as I can see. Do the China engineers brake physics low?
@graceho994 жыл бұрын
Nice video and precious info one can rarely find. One question: when you say that in the 24v inverter, the 24v DC input is turned into 18v AC before it enters the transformer, is the 18v in terms of RMS (i.e. voltage one reads from a volt meter)? Or you are talking about peak voltage?
@fabriziobrutti12053 жыл бұрын
It's RMS
@awade76225 жыл бұрын
Great video !
@geocha19625 жыл бұрын
Do you know the current limit on the DC site for each ? Thanks George
@Rafaeljotiar4 жыл бұрын
48VDC input with how much wattage input to get high wattage ?
@tonyolomu114 жыл бұрын
Hi morning I just wanted to know so if you can on couple a Sunny Boy 2000 W Solar PV grid tied Inverter 2000HF SMA SB2000HF-30 2KW. To a 15kw 48v power jack inverter, running the AC output from the inverter into to the AC input of the power jack inverter so that it can charge the batteries and also so run back into the power panel of the house please let me know and it is for the UK market thanks
@BonitaCreekWaterGuy6 жыл бұрын
I have a Aims 10kw 48v split phase that was working for the last 3 years. Three in the morning lighting hit somewhere close and took out the inverter. Does the Power Jack have surge protection? The Aims 10kw needs a 15kw generation and I have a 7.5 kw so I never hooked it up. What does the Power Jack require for a generator connection?
@GenetrySolar6 жыл бұрын
I can tell you that I accidentally sent the grid through my inverter and it roasted the breaker but the inverter was fine. They use 70 amp push button reset fuses that seem to work great.
@nsacrooks5 жыл бұрын
What happened to the inverter carcass? I am an electronic technician. Might be interested in your blown inverter as a project.
@GenetrySolar5 жыл бұрын
Inverter carcass?
@nsacrooks5 жыл бұрын
Did you repair your inverter? If not I'd like to attempt repair of it.@@GenetrySolar
@alexysortiz96835 жыл бұрын
What is the fan voltage rated on 5000w 24v powerjack? 24v? I can only took 3100w out of it before the fuse blow, upgrade the fuse??
@GenetrySolar5 жыл бұрын
Do you have a split phase version?
@alexysortiz96835 жыл бұрын
@@GenetrySolar nop, just 1 phase at 110v
@paywaldo21035 жыл бұрын
I don't know much about these inverters, so take this with a grain of salt..... Do you know if the 5kw rating is peak or RMS? 5k/sqrt(2) = 3.5k which is close to where your fuse is blowing. Some companies boast a little on wattage (at least with speakers and amps), I have no idea about your inverter company. Still seems like you shouldn't be blowing a fuse though. I would contact the manufacturer and also see what they think. It's hard to say increase the fuse size, because something else inside could get damaged by the current that is blowing your fuses. some appliances draw in a large inrush of current initially and then average out much lower. not sure if that could be a cause. Good luck!
@SuperVstech5 жыл бұрын
Alexys Ortiz my understanding of the 110v models is limited single circuit wattage . The fuse is likely seeing far beyond amperage due to induction surge. Motors pull much more watts than resistance loads.
@michaelbatchelder4 жыл бұрын
Is Power Jack the brand? Can't find them listed, maybe out of business since this is a 2018 video
@faidularcs5 жыл бұрын
It's reviews!
@Migueldeservantes5 жыл бұрын
Does the 2019 models have a higher voltage AC on the input?? I mean I would love to use the 48 but that would put me on a purchase of an extra set of 12 batteries of 2V "1100" amp batteries.. and that my friend is in the order of the 5K..... your advice will be greatly appreciated.
@BonitaCreekWaterGuy6 жыл бұрын
Is the 48v. split phase a pure sine wave? Have you tested the sine wave? I need 60 Hz and the Aims was a steady 59.7 Hz and no adjustment. Does the Power Jack have an adjustment? Does this have a bonded neutral or a floating neutral?
@GenetrySolar6 жыл бұрын
It is a perfect 60hz. It also has a floating neutral, however when connected to the breaker neutral it will share the bond. Floating neutral only applies to the outlets on the front.
@MMA.Indonesia2 жыл бұрын
where to buy it
@user-bi5sd4ct3s4 жыл бұрын
This is a question from Japan Where is the product purchased from, for example, a website? Please tell me the site address. Please tell me the price Thank you.
@ImpalaSSRulz214 жыл бұрын
EBay. Power jack inverter
@user-bi5sd4ct3s4 жыл бұрын
This is a question from a Japanese. Where can I buy this product?
@huuqua89454 жыл бұрын
Please buy that inverter link
@harnamchand5 жыл бұрын
I want a 15 Killo Watt Inverter input 24 Volt DC To AC 220-240, 15000 Watts. How much Price US Dollars
@anazmy4 жыл бұрын
Where can I buy inverters
@fredschreffler48695 жыл бұрын
How much does a 48 volt inverter cost
@daythunder12 жыл бұрын
Seems like I bought my 12 volt power jack inverter for nothing. No way to upgrade my 12 volt to 24volt or 48volt... ☹️🙄😢 $$$ down the drain
@timturner65484 жыл бұрын
Can carry amp better
@greatogbuagu13705 жыл бұрын
Which is better, 48 volts or 24 volts and why?
@GenetrySolar5 жыл бұрын
48 volts will always be better. Less heat because fewer amps to get to 120 volts. Less strain on the inverter.
@gottamodify77565 жыл бұрын
Is this a true 15kw inverter, and is it 7.5kw per side.
@GenetrySolar5 жыл бұрын
Yes true. At it's Max. I would stay closer to 6k per side max if you want it to run continuously.
@troy50075 жыл бұрын
Can you run the powerjack inverters in parallel? Thanks for your help.
@jec_ecart4 жыл бұрын
Who the heck makes 15kwa in 24v???? They must be atleast 96v
@bernardotabaranzajr76525 жыл бұрын
What is the best brand of pure sine wave inverters that you can recommend to be used to light up the off grid house?
@elijahhannigan14754 жыл бұрын
out back
@africantech52 жыл бұрын
Famicare
@victorrinz37535 жыл бұрын
15000/48 presque 400amp les batterie vent exploser
@rynoopperman50104 жыл бұрын
I don’t understand the vid Spend all this time explaining why gas powered engine can’t be converted to a diesel engine... Why spend time on this?
@elixier335 жыл бұрын
Its clearly 220v not 240v! Its written on the front!
@mdnazmul-mianazmul14015 жыл бұрын
12v & 24v good..! 48v no good. How to make device 12v & 24v inverter system power supply. & 24 hour.! it's very important. I want this device to be make.!this Device 24 hour backup...? & full load.? Thank you guys. for this your watching.
@pogpogcasino5 жыл бұрын
Lol. The higher the voltage the lesser the current drawn. 48 or higher is best. 12 volt & 24 volt will be drained faster than 48 volts.